|
We are converting a 1930s church to a live music venue. To prevent noise, we are sealing the roof in the attic and insulating the ceiling in the attic.
The fire sprinkler pendants were installed through the existing plaster ceiling with oversized bore holes. Additionally, the pendants have a metal collar with 4 integral slots. Is it permissible to seal the oversized bore hole? Is it permissible to seal the upper terminus of the slotted metal collar? We're not looking to violate code but address the sound needs. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Casey Milhorn
5/23/2025 08:20:07 am
Hard to tell from the picture, but it appears it might be a concealed pendent. If so, you cannot seal on the finished ceiling side where the concealed plate is. Anything that could keep the plate from "falling away" should be avoided. Other types of escutcheons generally are okay to seal around, but for maintenance purposes it would be best to install any sound caulking/materials on the unfinished side of the ceiling and make sure it doesn't come in contact with the concealed plate. Also, if it is a concealed head, you might consider a clean room seal option, if available. They aren't overly expensive and could help cut down some on sound transmission. The seal should be listed with the concealed plate, which should be listed for that specific sprinkler pendent. The entire assembly must be listed.
Reply
Glenn Berger
5/23/2025 08:29:33 am
Need to take care to not to damage the operation integrity of the sprinkler.
Reply
Zack Hinson
5/23/2025 08:31:53 am
Concealed sprinklers penetrations are not allowed to be sealed. NFPA 13 2019 16.2.5.4. Also the holes in the top of the concealed pendent are there specifically to get heat to come up into the sprinkler compartment and removing the draft from the heat could remove the listing of that sprinkler.
Reply
Jesse
5/23/2025 08:39:39 am
That's a pretty big "no".
Reply
Dan Wilder
5/23/2025 08:47:09 am
Yes, No, and with care....
Reply
Chris
5/23/2025 10:34:38 am
Wild shot in the dark... What if you took a red solo cup, cut it in half and cut the middle out (so if could fit around the pipe), then taped it around the pipe (upside down) on the topside shown in the photo. Then, took expanding foam insulation and encased the cup.
Reply
Adam Jensen
5/23/2025 11:13:59 am
I'm wondering if a dry barrel boot would do the trick (or be allowed)...
Reply
5/26/2025 12:23:20 am
Thanks for all the comments and advise.
Reply
Warren
5/28/2025 11:21:02 am
If you are just looking for sound attenuation, wrap the pipe (above the ceiling) with rock wool insulation that is thick enough to cover the annual space, snug it down to the top of the ceiling, then put a hose clamp around the upper portion of the insulation to keep it in place. This will not interfere with the clearance around the sprinkler head or the performance of the sprinkler system.
Reply
Joseph Wright
5/28/2025 10:07:30 am
I would recommend using a Tyco Dry pendent boot.
Reply
6/9/2025 07:48:11 pm
The client has agreed to use the dry pendant boot
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
