Non-Expanded Plastic as Class IV or Group A?

8/13/2026

9 Comments

 
I've got a question regarding commodity classification in a facility with a sprinkler system designed for Cartoned non-expanded Group A Plastics.

The owner wants to store high-weight non-combustibles inside plastic containers, see picture. 
Picture
The total weight of plastics will not exceed 15% of the total weight.

Is there any chance the storage unit can be treated as a Class 4 commodity and raised to Cartoned Group A Plastics due to the plastic pallet?

Or is it necessary to treat the commodity as Exposed Group A Plastics because of the plastic container? 

Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Peter H
8/13/2026 07:14:19 am

What type of plastic is the container made out of?

Reply
Glenn Berger
8/13/2026 08:33:06 am

As an AHJ told me early in my career - I see plastic; the entire system design must be for the exposed plastic.

Reply
Jesse
8/13/2026 08:37:41 am

Yeah I gotta go with Group A Plastic.

Reply
Joe Mc
8/13/2026 09:02:16 am

Unless you can prove that its class 4 go with Group A plastic.

I always ask my self do I want to make the NEWS for a place that burns down or had a small fire and the fire sprinkler system worked.

Reply
Jack G
8/13/2026 09:40:44 am

Under nfpa 13 plastic containers and the products inside are classified based on the resin type ( group A,B, or C) whether the plastic is expanded or non expanded and whether the containers are considered cartooned or exposed.
Group A: high hazard materials such as ABS, HDPE, polycarbonate, polyester, polypropylene, polystyrene, polyethylene.
Group B and C: B includes, cellulosic materials and acrylics..
C includes flouriplastics, melamine, and PVC , WITH low plasticizer content ( treated as class 3 commodities.
Expanded vs Nonexpanded:
Expanded plastics contain cellular or foam cavities trapping higher risk ( air) ; nonexpanded have a solid density like " molded storage bins ".
Cartooned vs exposed -- per nfpa 13 cartooned strictly as storage fully enclosed in corrugated cardboard or paperboard. Because group A plastics do not absorb water group A plastics inside or utilizing plastic containers are " generally " classified as exposed rather than cartooned.
Free flowing or cartooned: small objects, powders, or loose plastic items inside are considered free flowing which impact chapter 20 requirements.
First you must define the resin type for the above container.

Reply
Dan Wilder
8/13/2026 01:04:03 pm

That is a packaging not the commodity. The fact its plastic makes it no different than storing with plastic pallets (and looking at the bottom, that is what the pallet is, and likely reinforced) so unless whatever being stored is a Class I or II commodity, you're automatically into Group A.

Second issue is these looks like a big bin, and looking at the data sheets on it, there is no requirement to keep a lid so are you protecting for encapsulated or nonencapsulated? Other issue is bin box is defined as wood, metal, or cardboard...not plastic so as Jack pointed out, exposed.

Reply
Jimmy
8/14/2026 01:49:22 am

Thanks for all the replys,
It seems like Group A exposed Plastics would be the right commodity classification. (the container is Polyethylene - Group A Plastic).

But I wounder when the following would apply?


Extraction from NFPA13 2025 (20.4.3.2):

Storage Involving Group A Plastics

Once it has been determined that the stored commodity that requires protection contains Group A plastic, the process of determining the commodity class, although sometimes confusing, can be broken down into simple steps.

The critical components used to determine the commodity classification are individual storage units (e.g., unit load, pallet load), the primary packaging material, and the pallet type and composition. A simple correlation can be formed—an individual load (such as a pallet load) takes up a volume of space and has a certain total weight. As the amount of plastic that makes the load increases, the severity of the fire and the protection criteria will also increase.

Confusion often occurs when it comes down to the percentages by weight or volume of Group A plastic that differentiate classification levels from a Class III all the way to an exposed expanded plastic. It is the weight and volume of the load, not the individual items in the load, that determine the classification.

Weight. The weight is often misapplied to the individual product rather than to the total load. Simply imagine the load (usually on a pallet) sitting on a scale—that is the total weight of the load. Some loads are individual units as they stand on their own, but the concept is the same: the total load that will burn as a unit has a weight. The weight of the total quantity of unexpanded Group A plastic will be measured against the total weight of the load to determine the percentage of plastic weight. Therefore, to calculate the percentage of weight or volume of the product, the following factors must be included:

- The product itself
- Internal packaging and material, such as any dividers or protective material
- External packaging material (if any)
- Pallet or shipping aid (if any)

Reply
Nimal Tissa Wijetunga
8/16/2026 11:02:47 am

As per the information provided in the question, this must be considered as Group A plastic (Exposed/unexpanded) for Wet pipe Sprinkler design in line with requirements of NFPA 13.

Reply
Franck
8/20/2026 08:49:12 am

It is to be considered as group A plastic, because the fire will predominantly develop and spread on the outside and the sprinkler will work ob the outside as well.
In the most optimistic evaluation, it would be similar to an encapsulated commodity, which is already a greater hazard than a simple class IV commodity.

An important thing to consider: when stored, the upper lid needs to be present. If not, it will be considered as open top container and the sprinkler systems are really challenged with open top containers (water from sprinklers remains in the container rather than flowing around and prewetting adjacent loads)

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT