No Sprinkler in Bathroom of Wood Construction?

8/4/2025

7 Comments

 
Per the 2019 edition NFPA 13, Section 9.2.4.1.1, you can omit fire sprinklers within a small bathroom not exceeding 55 square feet that have walls and ceilings of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating.

Now
, if you read further down in section 9.2.4.2 relating to closets and pantries, it states, "surfaced with noncombustible or limited-combustible materials.

So in section 9.2.4.1.1, are we talking about the sheetrock walls and ceiling or the construction of the walls and ceiling?

If the bathroom walls and ceiling are constructed of wood but are covered with sheetrock, are the sprinklers still allowed to be omitted?

​I think it's confusing when they specify "surfaced with" when they are talking about the closets and pantries. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
8/4/2025 07:44:02 am

Let's check it out.

From NFPA 13 (2019 Ed.)

9.2. Allowable Sprinkler Omission Locations
9.2.4. Dwelling Units
9.2.4.1 Bathrooms
9.2.4.1.1* Unless sprinklers are required by 9.2.4.1.2 or 9.2.4.1.3, sprinklers shall not be required in bathrooms that are located within dwelling units, that do not exceed 55 sq. ft. in area, and have walls and ceilings of noncombustible or limited combustible materials with a 15 minute thermal barrier rating, including the walls and ceilings behind any shower enclosure or tub.
9.2.4.1.2 Sprinklers shall be required in bathrooms of limited care facilities and nursing homes, as defined in NFPA 101.
9.2.4.1.3 Sprinklers shall be required in bathrooms opening directly onto public corridors or exitways.
9.2.4.2* Closets and Pantries. Sprinkelrs are not required in clothes closets, linen closets, and pantries within dwelling units in hotels and motels where the area of the space does not exceed 24 sq. ft and the walls and ceilings are surfaced with noncombustible or limited-combustible materials.

A.9.2.4.1.1 A door is not required to omit sprinklers as long as the bathroom complies with the definition for compartment.
A9.2.4.2 Portable wardrobe units, such as those typically used in nursing homes and mounted to the wall, do not require sprinklers to be installed in them. Although the units are attached to the finished structure, this standard views those units as pieces of furniture rather than as a apart of the structure, sprinklers are not required.

--

Okay, so first thing: 9.2.4.2 does not apply to bathrooms. It only applies to closets and pantries in hotels and motels of less than 24 square feet.

So yeah, in your example where




9.2.4.2 is for closets and pantries. It does not apply to bathrooms.

So if the sheet rock provides a 15 minute thermal barrier and completely encapsulates the room (covers the walls and ceilings to a point that there is a 15 minute thermal barrier between the room and any combustible structural elements) and the room is a dwelling unit less than 55 square feet, you may omit. Otherwise, due to the wood structural construction (or the square footage or the fact it's not in a dwelling units), you need sprinklers.

Reply
Brett
8/4/2025 08:10:14 am

9.2.4.1.1 is not referring to the actual construction materials of the wood structure, but is referring to the surface material (drywall) that's providing the 15 minute thermal barrier.

The reason those two sections are written differently is because of bathtubs. You can build a bathroom that is surfaced with noncombustible or limited-combustible materials and not carry the drywall all the way around the backsides of the tub. This should always be coordinated prior to construction if you're planning on omitting sprinklers in bathrooms.

A closet or pantry won't have that issue, so it just says "surfaced".

Reply
Anthony
8/4/2025 08:46:34 am

Great call on the surround backing here! Many instillations call for a surround to be glued to OSB and then she rock to the lip of the top of the surround. This would NOT have a fire barrier as discussed. Check your arch details prior to omission.

Reply
Todd E Wyatt
8/4/2025 08:22:05 am

SUMMARY
IBC-2024
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.3.1 Standards
903.3.1.1 NFPA 13 Sprinkler Systems
903.3.1.1.2 BATHROOMS
In Group R occupancies sprinklers shall NOT BE REQUIRED in bathrooms that do NOT EXCEED 55 SQUARE FEET (5 m2) in area and are LOCATED WITHIN INDIVIDUAL DWELLING UNITS OR SLEEPING UNITS, provided that WALLS AND CEILINGS, including the walls and ceilings behind a shower enclosure or tub, are of NONCOMBUSTIBLE OR LIMITED-COMBUSTIBLE MATERIALS WITH A 15-MINUTE THERMAL BARRIER RATING.

EXPLANATION
The scoping Code (e.g. IBC-2024) determines WHERE an automatic sprinkler system (ASPS) is required ... 

IBC-2024
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.2 the
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.

... based on Occupancy Classifications (OC) ...

903.2.1 Group A
903.2.2 Group B
903.2.3 Group E
903.2.4 Group F-1
903.2.5 Group H
903.2.6 Group I
903.2.7 Group M
903.2.8 Group R
903.2.9 Group S-1
903.2.10 Group S-2 Parking Garages

... and based on Specific Building Areas and Hazards ...

903.2.11 Specific Building Areas and Hazards
903.2.11.1 Stories Without Openings
903.2.11.2 Rubbish and Linen Chutes
903.2.11.3 Buildings 55 Feet or More in Height
903.2.11.4 Ducts Conveying Hazardous Exhausts
903.2.11.5 Commercial Cooking Operations
903.2.11.6 Other Required Fire Protection Systems

... and lastly during construction :

903.2.12 During Construction

The scoping Code references the ASPS standards (e.g. NFPA 13) that includes HOW the ASPS is to be designed & installed :

903.3 Installation Requirements
Automatic sprinkler systems shall be designed and installed in accordance with Sections 903.3.1 through 903.3.8.
903.3.1 Standards
Automatic sprinkler systems shall be designed and installed in accordance with Section 903.3.1.1 unless otherwise permitted by Sections 903.3.1.2 and 903.3.1.3 and other chapters of this code, as applicable.
903.3.1.1 NFPA 13 Sprinkler Systems
903.3.1.2 NFPA 13R Sprinkler Systems
903.3.1.3 NFPA 13D Sprinkler Systems

Lastly, the scoping Code includes ASPS exemptions per the following, including BATHROOMS :

[F] 903.3.1.1.1 Exempt Locations
Automatic sprinklers shall not be required in the following rooms or areas where such rooms or areas are protected with an approved automatic fire detection system in accordance with Section 907.2 that will respond to visible or invisible particles of combustion. Sprinklers shall not be omitted from a room merely because it is damp, of fire-resistance-rated construction or contains electrical equipment.
1. A room or space where sprinklers constitute a serious life or fire hazard because of the nature of the contents, where approved by the fire code official.
2. Generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.
3. Rooms or areas that are of noncombustible construction with wholly noncombustible contents.
4. Fire service access elevator machine rooms and machinery spaces.
5. Machine rooms, machinery spaces, control rooms and control spaces associated with occupant evacuation elevators designed in accordance with Section 3008.

903.3.1.1.2 BATHROOMS
In Group R occupancies sprinklers shall not be required in bathrooms that do not exceed 55 square feet (5 m2) in area and are located within individual dwelling units or sleeping units, provided that walls and ceilings, including the walls and ceilings behind a shower enclosure or tub, are of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating.

903.3.1.1.3 Lithium-Ion or Lithium Metal Batteries

Reply
Jack G
8/5/2025 11:06:37 pm

Not sure the question was answered above.
Bathrooms with rated specified construction and ceiling, can be omitted if there are combustibles above the rated ceiling when the ceiling is attached or within 6 inches of the wood/ combustible joists.

Reply
Muhammad Munir Malik
8/6/2025 10:50:36 pm

very nice Information thanks to all,,,,
one my question in record room important documents safe can we install the sprinklers system or other fire suppression system please guide me thanks

Reply
OSAMA MINHAS
7/7/2026 12:30:08 am

In the context of hospitals i.e. patient care areas or Group-I2, sprinklers are required in bathrooms regardless of their size.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT