I'm designing a 13R system. The building currently has a 3/4" domestic water service. The building is in a location that would make installing a new (larger) service a logistical nightmare.
Is it allowed to connect the 3/4" existing supply to a water storage tank (sized per system/domestic demand) in the basement, then build a residential riser from that? If this is allowed, do I only take my calculations back to the storage tank? Do you foresee other problems with this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
5/6/2025 06:20:21 am
I'd do the tank with a small residential pump (something like the viking/econo residential pump, but listed for 13R. That pump is only for 13D systems) if I was that worried about the water supply.
Reply
Karl
5/7/2025 09:39:45 am
Yes, it will require a 13R pump/tank system. The hydrant test shows good pressure and volume, but it's only a 3/4" line coming in for domestic, so the calcs have to include domestic demand.
Reply
Jesse
5/6/2025 10:14:05 am
13R is the issue here. 13D is a lot more forgiving. There are a lot of pump / tank combos listed for 13D thata don't carry al isting for 13R. Any tank you install for a 13R design will need to meet NFPA 22 requirements
Reply
Karl
5/7/2025 09:34:19 am
Yes, the owner will need a 13R pump/tank system. Thanks for the input!
Reply
5/6/2025 10:37:52 am
What type building is this? Single family dwelling? Because if it's 13D, you'd be fine, but if it truly is a multifamily/multi-story dwelling under 13R, that's not likely going to fly.
Reply
Karl
5/7/2025 09:30:11 am
So this was a small 2 story office bldg w/basement that is being converted to 6 apartments.
Reply
Jack G
5/6/2025 12:22:05 pm
I m not sure what you are describing.
Reply
Karl
5/7/2025 09:33:07 am
Thanks for the input, it will be 13R system, now I just have to tell the owner he's gotta' buy a 13R pump/tank system! & yes, it will be a 4 hd calc. Again, thanks for your input
Reply
Wes
5/7/2025 09:39:00 am
Just be careful; a Fire Pump for NFPA 13D does not need to meet NFPA 20.
Reply