MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

NFPA 101 (1-hr) or NFPA 90A (2-hr) in 4-Story Shaft?

1/21/2025

11 Comments

 
NFPA references are based on current editions. While NFPA 101, Section 30.3.1.1.4 (New Apartments) allows vertical penetrations to be protected with a 1-hour rating when sprinklered, NFPA 101, Section 30.5.2 requires HVAC equipment to comply with NFPA 90A.

According to NFPA 90A, Sections 9.1.3 and 6.8.3, a higher level of protection is required for shafts that penetrate more than four floors (2-hr fire rated and fire dampers).

Does the exception provided in NFPA 101 permit reducing the required fire rating to 1-hour for duct shafts, or does NFPA 90A take precedence?

I'm curious to hear different perspectives on this.

I can understand both sides of the issue but find it challenging to justify allowing a 1-hour fire rating for a vertical exit within a New Apartment while requiring a 2-hour fire rating for the duct shafts.


Thanks in advance.
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Christopher Nelson
1/21/2025 08:22:05 am

I would say this is similar to other situation where this accounting for building construction rather than stories. NFPA 101 7.1.3.2.1 requires exits 4 or more stories to be 2 hrs unless and existing building which you are not.

Im thinking this more for a Type IA/IB/IIA 3 story structure rather than 4 or more stories apartment.

Go with the normal 2 hr when connecting 4 or more stories.

Reply
Ricardo Gonzales Jr
1/21/2025 08:45:50 am

If both NFPA documents are adopted by the jurisdiction, most AHJs would use the more stringent of the two. Note the 1st word of the sentence above. It also depends on the AHJ on which department owns the building and its ratings vs. a single department responsible for it all. If it's compartmentalized, it could be the responsibility of the Mechanical, Architect or Fire Life Safety.

Reply
Pete D
1/21/2025 09:18:48 am

I'd like to echo this with caution. NFPA 101 is not adopted by all jurisdictions, and it differs from IBC. I also want to comment, if your structure is IA, as classified by Table 601 IBC and the jurisdiction is on IBC, you have a 2 hr slab rating. The vertical duct can be "shafted", which I guess is jargon/vernacular for wrapped in fire rated material to carry the rating for the slab up to the next slab. That could mean 2 layers of 5/8 type X gypsum on a minimum 3 5/8 stud wall with base of wall and head of wall fire stopping, or a 2-hr shaft wall around the duct. Typically, we're cladding the duct for aesthetics anyway. I caution that the devil is in the details. You need to ensure for a conventional wall you're using UL, cUL, or Intertek or some listing agency recognized by your jurisdiction. My last comment is, in IA construction the slab penetration must have a T, F, and L rating. Understand the difference. It must block fire, temperature increase, and the leakage of air/smoke. Fire dampers come in 1.5 hr and 3 hr, and you will use the 90 minute fire/smoke damper for the 2 hr rating. They make butterfly dampers that are inside the duct beneath the slab penetrations that operate on mechanical links and torsion springs. These are ideal if it's a bulk run of duct without any branch offs. Otherwise, if the duct is wrapped in fire-rated material, any tributaries that branch off on the intervening floors will need fire-smoke dampers, which require mechanical actuation of the fire component and electronic actuation of the smoke component with a duct detector installed within 5 feet of the damper.

Reply
Todd E Wyatt
1/21/2025 09:08:17 am

If (only) NFPA 101 Life Safety Code - 2024 (LSC) is the adopted, scoping Code for this Project, LSC takes precedence over Referenced Publications per Chapter 2 :

LSC
Chapter 2 Referenced Publications
2.1 General.
The documents referenced in this chapter, or portions of such documents, are referenced within this Code, shall be considered part of the requirements of this Code, and the following shall also apply:
(1)*Documents referenced in this chapter, or portion of such documents, SHALL ONLY BE APPLICABLE TO THE EXTENT CALLED FOR within other chapters of this Code.
(2) Where the requirements of a REFERENCED CODE OR STANDARD DIFFER from the requirements of this Code, the requirements of this Code shall GOVERN.

2.2* NFPA Publications.
NFPA 90A, Standard for the Installation of Air-Conditioning and Ventilating Systems, 2024 Edition.

NFPA 90A is referenced (32) times in LSC but NOT in the sections prescribing the fire-resistance rating (FRR) for shafts :

LSC
Chapter 8 Features of Fire Protection
8.6 Vertical Openings.
8.6.4 Shafts.
Shafts that do not extend from the bottom to the top of the building or structure shall comply with 8.6.4.1, 8.6.4.2, or 8.6.4.3, as modified by 8.6.4.4 or 8.6.4.5.
8.6.5* Required Fire Resistance Rating.
The minimum fire resistance rating for the enclosure of floor openings shall be not less than as follows:
(1) Enclosures connecting four or more stories in new construction shall be 2-HOUR FIRE BARRIERS.
A.8.6.5
The application of the 2-hour rule in buildings not divided into stories is permitted to be based on the number of levels of platforms or walkways served by the stairs.

NFPA 90A is only referenced in Chapter 8 Features of Fire Protection per the following :

8.5.5.4 Installation, Testing, and Maintenance.
8.5.5.4.1
Air-conditioning, heating, ventilating ductwork, and related equipment, including smoke dampers and combination fire and smoke dampers, shall be installed in accordance with NFPA 90A, NFPA 90B, NFPA 105, or NFPA 80, as applicable.

Reply
Jordan
9/17/2025 08:47:09 pm

Received some additional clarification from NFPA on this. Todd E Wyatt hit the nail on the head.

Yes, the HVAC shaft can have a 1- hour rating. NFPA 101, Section 2.1(2) states that NFPA 101 will take precedence over other standards that have differing requirements. Therefore, HVAC shafts can comply with the requirements of 30.3.1.1.4.

Reply
Jeff Ayers link
1/21/2025 09:41:26 am

The NFPA design standards appear to be driven by IBC building classifications. For wood Apartments its primarily Type VA & VB (4 stories or less) & Type IIIA and IIIB 5 stories of wood.

You wrote: "shafts that penetrate more than four floors (2-hr fire rated and fire dampers)" more than 4 floors places you in a Type IIIA with the exterior load bearing wall 2 hours, vertical shafts are 2 hours, steel protection is 2 hours etc., floors are 1 hour.

While Type IIIB allows combustible material on the floors and roofs (FRT not required) the floors still have 1 hour rating for penetrations similar to VA & VB.

Floor to floor penetrations (vertical openings) are typically 1 hour even though mechanical duct shafts are 2 hours.

Your question appears to be confusing 3 different terms:
Vertical openings are penetrations in the rated floor.
Shafts are rated enclosed openings around holes in the floor.
Vertical exits are stairwells with 2-hour walls (typically). Type IIIA has 3-hour walls separating the floor areas and usually has a shared wall at the stair / demising wall.

Maybe you can clarify your question, because the codes you reference do not seem to get to the heart of your question.

Reply
Jose R Figueroa
1/21/2025 11:57:43 am

The difference comes down to how NFPA 101 and NFPA 90A approach safety. NFPA 101 offers a bit more flexibility—if you install sprinklers, you might be able to reduce ratings a bit. On the other hand, NFPA 90A takes a stricter stance when it comes to HVAC shafts because they can quickly spread fire and smoke between floors. It's all about finding the right balance for fire & life safety. Consult your AHJ.

Reply
Jose R Figueroa
1/21/2025 12:42:58 pm

I must include NFPA92 in the discussion. The HVAC system should also be a smoke control system. The HVAC system should be built according to NFPA 90 and 92. It will meet NFPA 101 requirements automatically.

Reply
Wes
1/21/2025 12:48:38 pm

An HVAC system for a four story building does not automatically become a smoke control system under NFPA 92. A smoke control system is far more involved than an HVAC system.

Jack G
1/21/2025 12:27:09 pm

Assuming it is not HT construction or roof is not 20 ft higher than the floors.
VA— construction does not allow 13r or 13 d systems.
VB — does not allow 13 r or 13d over 2 stories.
Also to reiterate LSC codes are not a part of NFPA 13. The NFPA 13 appendix addresses that 101 is not a part of the 13 standard.
Also there are certain size closets that 101 permits you not to protect with sprinklers. This is not permitted.
Any area increases or fire rating reductions are also not permitted by the IBC.
Review the IBC commentary section sheet that charts what type system is permitted, 13, 13r, or 13 d.
There are also superscript notes that indicate ( as long as protection is extended into the area ( open wood joist s between floors, attics, balconies etc)
As HVAC floor penetrations allow exposure to all floors, thru the shaft, the rating reductions of the shafts and floors would not be allowed. ( personally, I would protect the top too, below the roof line— dry sidewall if unheated)
So it basically depends on how the building is constructed.

Reply
Mike
11/19/2025 08:54:07 am

I’m working in a multi family apartment and it has a 10 x 10 dryer duct 2 hour fire rated shaft. My blue print show a 4” 90 with 22” pipe up inside the shaft. Will this cause lint buildup and a fire. Is this Method recommended.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT