New Storage Tenant Need to Meet Current Code?

9/16/2025

10 Comments

 
If a warehouse is getting a new tenant, and the AHJ requires a new C of O, does the sprinkler system need to meet current standards (NFPA 13-2022) or can the original standards (NFPA 13-2007) be used?

Specifically looking at Group A plastic protection requirements here. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
9/16/2025 06:09:01 am

This can depend on a number of things from local ordinances to the amount of building renovation the new tenant is doing within the warehouse.

Reply
Tom
9/16/2025 08:27:18 am

The new tenant/building owner needs to submit a storage/commodity report from a fire protection engineer. In short prove to me that the sprinkler system is adequate for what ever manufacturing or storage in intended for that building.

Reply
Dan Wilder
9/16/2025 08:33:05 am

AHJ and building specific.

Most of my AHJ's, in storage applications, would require a reevaluation of the water supply and system capabilities as the storage rules have changed so much over the years.

Perfect example is Speculative Warehouses were all designed to a 0.495/2000 (Class IV to 20', conventional pallets, high temp sprinklers), the current requirement is 0.60/2000 (Group A Plastics to 20', high temp sprinklers)....big jump. I know your question was for ESFR specifically but without knowing the original design vs current requirements, it could be an issue.

Reply
NK
9/16/2025 08:43:28 am

Great question and lots to talk about here. There's another similar post from 2023 about this:

https://www.meyerfire.com/daily/did-removed-esfr-design-criteria-fail-testing

My take:

1) Change tenants doesn't require a system modification, but changing the use or process of the space may require system modification (even if it's the same tenant) because fire sprinkler systems are specifically designed for the use of the space being protected.
2) I know all states don't adopt NFPA 1, but NFPA 1, 2018 §13.3.3.4.1.6 "Changes in Occupancy, Use, Process, or Materials" addresses this.
3) Reading the "Purpose" and "Retroactivity" sections of NFPA 13 are useful in understanding what we're trying to do with fire sprinkler systems. If the requirements slightly changed between editions, you have the original fire sprinkler drawings and calculations, and you verify the water supply hasn't changed I think it's reasonable to talk to the AHJ and insurance company about allowing the old system to stay so if/when there's a fire everyone is on the same page.
4) If there are huge changes in the NFPA 13 requirements, it very possible that new fire testing showed the old requirements to be less effective than previously thought in which case I would not recommend holding the liability to say that the existing system is OK because it met 2007 requirements when it's not going to control an actual fire. Group A plastics have the highest heat release rate so this isn't something I would recommend endorsing because it's not "clearly evident that a reasonable degree of safety is provided".


NFPA 13, 2022 §1.2 Purpose
§1.2.1 The purpose of this standard shall be to provide a reasonable degree of protection for life and property from fire through standardization of design, installation, and testing requirements for sprinkler systems, including private fire service mains, based on sound engineering principles, test data, and field experience.
§1.2.2 Sprinkler systems and private fire service mains are specialized fire protection systems and shall require design and installation by knowledgeable and experienced personnel.

NFPA 13, 20221.4 Retroactivity.
The provisions of this standard reflect a consensus of what is necessary to provide an acceptable degree of protection from the hazards addressed in this standard at the time the standard was issued.
§1.4.1 Unless otherwise specified, the provisions of this standard shall not apply to facilities, equipment, structures, or installations that existed or were approved for construction or installation prior to the effective date of the standard. Where specified, the provisions of this standard shall be retroactive.
§1.4.2 In those cases where the authority having jurisdiction determines that the existing situation presents an unacceptable degree of risk, the authority having jurisdiction shall be permitted to apply retroactively any portions of this standard deemed appropriate.
§1.4.3 The retroactive requirements of this standard shall be permitted to be modified if their application clearly would be impractical in the judgment of the authority having jurisdiction, and only where it is clearly evident that a reasonable degree of safety is provided.

Reply
Todd E Wyatt
9/16/2025 08:52:31 am

Start with the International Existing Building Code (e.g. IEBC-2024) and go to …

Chapter 10 Change of Occupancy.
Section 1011 Change of Occupancy Classification
1011.2 Fire Protection Systems
1011.2.1 Automatic Sprinkler System
The installation of an automatic sprinkler system shall be required where there is a change of occupancy classification and Chapter 9 of the current International Building Code requires an automatic sprinkler system based on the new occupancy or where there is a change of occupancy within the space where there is a different fire protection system threshold requirement in Chapter 9 of the current International Building Code than exists in the current building or space. The installation of the automatic sprinkler system shall be required within the area of the change of occupancy and areas of the building not separated horizontally and vertically from the change of occupancy by a nonrated permanent partition and horizontal assemblies, fire partition, smoke partition, smoke barrier, fire barrier or fire wall.

If the automatic sprinkler system (ASPS) is required per it’s new Occupancy Classification (OC) per the adopted scoping Code (e.g. IBC-2024) per the following …

Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.
903.2.1 Group A
903.2.2 Group B
903.2.3 Group E
903.2.4 Group F-1
903.2.5 Group H
903.2.6 Group I
903.2.7 Group M
903.2.8 Group R
903.2.9 Group S-1
903.2.10 Group S-2 Parking Garages
903.2.11 Specific Building Areas and Hazards

... then the existing ASPS is required to meet the referenced NFPA 13 edition (e.g. NFPA-2022) per the adopted scoping Code.

Reply
Brett
9/16/2025 09:54:09 am

The problem with this approach is that it isn't typically a change in occupancy. Usually it's an S-1 building being occupied by another tenant still using it as an S-1 occupancy. The second tenant might be stuffing it with higher hazard materials, but not hazardous enough to classify the space as group H.

Reply
Rick
9/16/2025 08:53:48 am

2007 to 2022 have major changes. Cartoned non-expanded group a plastics should be similar, but cartoned expanded and exposed non-expanded have bigger changes. I wouldn't group all "Group A plastics" together if you're looking into this.

Reply
Jose R Figueroa
9/16/2025 10:49:20 am

The new tenant may change the storage class, so we must perform a comprehensive engineering analysis. Relying solely on the existing code without a proper assessment could pose a risk of a catastrophic fire. I remember 50 years ago, a tissue paper storage facility burned to the ground despite having an “adequate” sprinkler system. The issue arose when the tissue rolls switched from paper to plastic wrapping.

Reply
Jesse
9/16/2025 01:32:10 pm

I'm going to defer to the AHJ on this. I would highly recommend them getting on board. At the very least I'd evaluate the extant protection and the water supply.

Reply
sean
9/18/2025 05:29:08 pm

if the building has lost the cert. of occupancy new regulations can apply

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT