Is there anything in NFPA 13 that states you cannot mix fusible link and glass bulb heads within the same area as long as both sprinklers are standard response?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Peter Howard
7/17/2025 06:18:26 am
There's no reason I can think of you can't as long as both sprinklers are the same response type.
Reply
Anthony
7/17/2025 08:13:57 am
Its perfectly legal, happens a lot with replacement heads.
Reply
Dan Wilder
7/17/2025 08:23:20 am
Matching response type (quick or standard) is the only requirement, see 13-19' 9.4.3.1 with the exceptions of Residential/QR sprinklers see 13-19 12.1.4 and use of sprinklers listed as SR but contain a QR operating element (9.4.3.5). The 22 edition has a new chart in 7.2.4.1 for Temp Ratings and Classifications that separate Glass Bulb and Link to assist in matching classifications between the two.
Reply
Glenn Berger
7/17/2025 08:55:59 am
As others have mentioned, as long as the characteristics are the same it is technically permissible. Possibly need to update the spare sprinklers that should be kept in the sprinkler cabinet and update some documentation.
Reply
Franck
7/17/2025 09:57:45 am
I confirm all of the above.
Reply
Chris Nelson
7/18/2025 06:36:23 am
Only thing is how big is the space? Warehouse size room, sure mix'em, as people said as long as temp and response type are the same.
Reply