We have a facility with an NFPA 13 Extra Hazard 1 sprinkler system.
The client's proposed location of the water storage tank is approximately 33-ft (10m) higher than the level of the protected building and around 100-ft (30m) away. The client's proposed pump house is closer to the building, separate from the tank. My question is - is there a maximum length for the suction feed from the tank to the pumphouse under NFPA rules (13, 20, 22)? I would rather locate the pump house next to the tank and run the delivery main to the building. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
9/10/2025 08:22:11 am
You need to compare the Net Positive Suction Head Required (NPSHr) vs Net Positive Suction Head Available (NPSHa).
Reply
Brian Gerdwagen FPE
9/10/2025 08:25:35 am
If the tank is higher than the pump, the only limit are your calculations.
Reply
Jesse
9/10/2025 08:25:36 am
Yeah agree with Glenn. You don't want the pump pulling water under a lift condition as you'd limit yourself to a vertical turbine pump.
Reply
Ryan Hinson
9/10/2025 09:44:52 am
Perform hydraulic calculations on this section of pipe IAW NFPA 20 (2022) Section 4.16.3 to determine size and allowable length:
Reply
Joseph Wright
9/10/2025 10:11:20 am
We completed a box store a number of years ago with a remote storage tank approx. 400' from the pump. For a 1500 GPM pump we had to upsize the underground main to 12" instead of 8" to get the suction above -3 psi
Reply
Mike Russell
9/10/2025 01:13:09 pm
Joseph is on the right track here. During System Acceptance testing, you need to run the pump at 150% of rated capacity (there is an exception to run at system demand if the water supply is not capable of acheiving the 150%).
Reply
Mark Harris
9/10/2025 11:55:33 am
All good comments. Soundsl like tank outlet wil be above pump so flooded suction and just have to deal withthe hydraulics as noted.
Reply
Jack G
9/15/2025 05:51:33 pm
Also depends where the bottom of the tank is.