Manage Storage of Lithium-Ion Vehicle Batteries?

4/28/2021

10 Comments

 
What are your recommendations for fire safety of single height storage of Lithium-ion vehicle batteries?

Currently in our warehouse, in a sprinklered covered area, we are storing 3 to 5 of these lithium-ion batteries before they are sent to dealerships. We have security guards take 1-hour temperature readings throughout the day and night but little else has been put in place and a proper fire risk assessment has not been performed. Thanks in advance.
​
​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Mike
4/28/2021 08:27:01 am

I am working on a massive project where there are massive quantities of these types of batteries being manufactured, stored and used. The owner had a Fire Protection Engineer prepare a risk assessment.

Consultants are quite expensive and maybe the AHJ will have their own requirement.

Reply
Thomas
4/28/2021 08:31:03 am

What design density? How high?

Reply
Dan Wilder
4/28/2021 08:44:03 am

NFPA 855 has a little guidance available.

Here is a list of NFPA links to their research
https://www.nfpa.org/ess

with this report being specific to sprinkler protection...
https://www.nfpa.org//-/media/Files/News-and-Research/Fire-statistics-and-reports/Suppression/RFESSSprinklerProtection.pdf

However, as Mike said above, these are emerging technologies and hiring a FPE to create a report taking into account what the building is doing for both active & passive protection (rated walls, containment, detection) in addition to providing sprinkler related protection design criteria will be your (the owners) best option.

Reply
CJ Bonczyk
4/28/2021 09:17:22 am

I agree with Dan. We have had these facilities pop up all over Texas. Many times the information regarding the storage layout, height, if they are contained or not, all needs to be long thought out prior to the sprinkler design and water availability. Currently NFPA 855 2020 is your go to for now. Hiring an FPE and heavy coordination with the AHJ must happen to properly CYA. We have had to use certain clean agents, revise storage and add cut off spaces. The water usage to suppress a fire of these type is immense. A single instance here in Texas involved a Tesla car that the batteries caught fire and majority of the damaged was caused in the first 10 minutes from the batteries and chain reaction and just to put the car fire out required almost 30k gallons of water.

4.11.2.1 Sprinkler systems for ESS units (groups) with a maximum stored energy of 50 kWh, as described in 4.6.2, shall be designed using a minimum density of 0.3 gpm/ft² based over the area of the room or 2500 ft² design area, whichever is smaller, unless a lower density is approved based upon large-scale fire testing in accordance with 4.1.5.

4.11.2.2* Sprinkler systems for ESS units (groups) exceeding
50 kWh shall use a density based on large-scale fre testing in
accordance with 4.1.5.

A.4.11.2.2 UL 9540A Installation Level Test, Method 1,
provides the data needed to determine if automatic sprinkler
design densities can be changed. A sprinkler density in excess
of 0.3 gpm/ft² can be necessary to provide an adequate level of protection, especially for some lithium-ion battery ESS designs. However, test results for some ESS designs and technologies indicate sprinkler densities less than 0.3 gpm/ft² could be acceptable. Equivalent test standards, as permitted in 4.1.5, might provide comparable data.

Ventilation during suppression is critical. Research has
shown that Li-ion batteries might continue to generate flammable gases during and after extinguishing. In addition, testing has shown that during sprinkler suppression, removal of
combustion and flammable gases emitted from the battery
significantly improves the effectiveness of the suppression.

Reply
Franck
4/28/2021 09:35:50 am

There is a difference when the batteries are being used (ESS) and then you can apply NFPA 855 (0.3 gpm/ft² based over the area of the room or 2500 ft²) and storage of batteries that are not being used (such as big storage facility).

In the case of storage of large quantities of lithium-ion batteries, the commodity classification should be considered as unexpanded plastic.
When stored in cardboxes, the classification is unexposed unexpanded plastic, and when no packaging material is present, it should be considered as exposed unexpanded plastic.

Lithium-ion batteries kept in storage area should not be charged at more than 50% of their full capacity. Fully charged lithium-ion batteries have a higher energy density and are at greater risk of generating significant heat from short circuiting related to internal defects.

The storage area should be kept at a temperature between 4 and 27°C (40-80°F) to limit the risk of thermal runaway from manufacturing defects or internal failures.

Reply
Vasu
1/4/2024 10:06:27 am

What are the criteria to store large quantities of Li battery pallets on the floor?

Reply
Franck
4/28/2021 09:39:12 am

If batteries (lithium ion) are being used, then you may consider the following.

To date there is no publicly available test data that confirms the effectiveness of any active fire protection for energy storage systems. Automatic sprinkler protection is recommended to limit fire spread to the surrounding structure, equipment, and building contents. See NFPA 855 for more details.

If a Li-ion battery overheats, hisses or bulges, the device should immediately be moved away from flammable materials and place it on a non-combustible surface.
If at all possible, the battery should be removed and put it outdoors to burn out. Simply disconnecting the battery from charge may not stop its destructive path.

For the most part, a lithium-ion battery fire can at best be cooled, contained and suppressed. Extinguishing a lithium-ion battery fire with 100% certainty is not always possible due to the unpleasant issue of thermal runaway.
Lithium-ion battery fires do not require oxygen to burn and can be considered by nature a chemical fire.

A small Lithium-ion fire can be handled like any other combustible fire.
For best result use a foam extinguisher, CO2, ABC dry chemical, powdered graphite, copper powder or soda (sodium carbonate).
A small module on fire can also be immersed into water. Water-based products are most readily available and are appropriate since Lithium-ion contains very little lithium metal that reacts with water. Water also cools the adjacent area and prevents the fire from spreading. Research laboratories and factories also use water to extinguish Li-ion battery fires.

For larger fires, specific extinguishers approved for lithium-ion battery fires, such as Lith-Ex extinguishers, should be used.
The portable fire extinguishers can be used for batteries installed inside equipment (mobile phones, tablets…) and where batteries are stored and/or are under charge.

Note that general class D extinguishers can normally only be applied to a flat surface as the extinguishant has no ability to adhere to vertical or other angular surfaces.
Copper based class D units, which are designed to cling to vertical surfaces, are also ineffective on lithium battery fires.
In the case of lithium-ion battery fires, these extinguishing agents have no ability to cool cells in order to prevent the propagation of the fire throughout a module.

A large Li-ion fire, such as in an Electrical Vehicle, may need to burn out. Water with copper material can be used. Using water even with large Li-ion fires is advisable as water lowers combustion temperature . But is not recommended for battery fires containing lithium-metal.

Reply
Franck
4/28/2021 09:40:16 am

Safety precautions
A safe separation distance should be maintained between battery charging stations and any combustible materials.
The minimum separation distance should be 0.9 m (3 ft) for large format batteries charging station and 0.3 m (1 ft) for small format batteries (such as the one used in tools).
Battery docking/charging stations should be positioned on a flat non-combustible surface.

As for any battery charger in storage areas, battery chargers for very large Lithium-ion batteries should be surrounded with a barrier which prevents any storage less than 1.5 m (5 ft) away.

Any Lithium ion battery with external visible damage should be replaced and the waste battery disposed in a dedicated waste bin. The internal integrity of a battery (components and mechanisms) is susceptible to high damages when subjected to external forces or dropped on a hard surface/ground.

Reply
Franck
4/28/2021 09:42:32 am

Used/damaged battery disposal
Battery terminals should be isolated (covered by insulation material) before disposal. This would prevent any accidental contact with metal or other battery contact that would close the battery circuit and result in energy discharge.
Batteries with physical or mechanical damages should be stored separately from other batteries.

A safe separation distance of at least 3 m (10 ft) should be provided between disposal of damaged/waste/discarded batteries and bins filled with other combustible material, or any combustible material.
Waste disposal bins for lithium-ion batteries should be made of metal (no plastic) and equipped with a metal lid.


Note that all the precautions listed in my comments are recommended best practices for lithium batteries. This not directly coming from a specific standard (but based on several sources of information).
To be adapted to you needs/point of view.

Reply
Clu Wright
2/20/2025 07:58:04 am

We have a power company proposing 200 Mgw of stored Lithium Ion Batteries in outside containers to power their substations. Has anyone had to review this type of storage and what was the requirements? we have a very busy State Highway and subdivisions nearby.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT