Main Drain for Fire Pump Room in Basement?

2/8/2019

12 Comments

 
I have a wet sprinkler system fed by a combined standpipe/sprinkler riser by municipal water with a "brand new" fire pump in the basement.

Where should the main drain be installed?

The municipal water enters the building and goes through the backflow preventer and then into the fire pump both being located in the fire pump room. After the fire pump, the riser goes to floor #1 and above. On the first floor there is a floor control valve with drain.

I explained to property manager that a main drain is required in the fire pump room to test the adequacy of the water supply and drain the system. The installer agreed with me but explained that is was not part of the drawing and he did not install one because he did not get paid for one.

The property owner consulted with the engineer of record who said that the main drain is not in the fire code. He also said his plans for the fire pump installation were approved by the Department of Building. He also consulted with other more experienced engineers in his firm and was told that no main drain is required on the fire pump piping or in the pump room, but if I wanted to drain the system or perform a main drain test I could do it from the first floor. 

Is a main drain in the basement fire pump room required?

Posted anonymously by a member for discussion. Discuss this  | Subscribe
12 Comments
Glenn
2/8/2019 10:18:11 am

Per NFPA-13 8.17.4.1 "Main drain test connections shall be provided at locations that will permit flow tests of water supplies and connections." There is not a specific location given, so the main drain test connection could be located on the first floor.

There does have to be a drain connection in the basement pump room though. NFPA-13 8.16.2.1 states "All sprinkler pipe and fittings shall be so installed that the system can be drained." So if there is no drain connection in the basement that is incorrect.

The main drain test is a qualitative test of water supply performance. It is performed annually to monitor for changes in the water supply.

Reply
MArk
2/8/2019 10:29:41 am

NFPA 20 2013 ed
4.12.7.2 Pump rom shall be provided with a floor drain that will discharge to frost free location

Reply
Mike
2/8/2019 10:31:36 am

I think the appropriate reference for the fire pump drain is NFPA 20.

Reply
vincent boves link
2/8/2019 08:04:25 pm

Hi Glen,
I agree with you that NFPA-13 8.17.4.1 gives no specific location. But being that the purpose of the annual main drain test is a qualitative test of the water supply performance basically to monitor for changes in the water supply, given that a fire pump has been installed in the basement of the building near the entry point of the water supply, and with all the check valves, and components between the basement and the "first floor" wouldn't it make more sense from a design standpoint to put the main drain in the basement, close to the water entry point for quick and better quality readings? As I pointed out to a colleague "if your need to scratch your right ear, it's best to use your right hand not the left hand" I really appreciate your help.

Reply
Mike
2/8/2019 10:30:38 am

If you have pdf of the standard, you can do a search for "drain"

NFPA 20

4.12.1.5 Provisions shall be made for discharge to a drain.

4.13.7* Drainage.
4.13.7.1 Floors shall be pitched for adequate drainage of
escaping water away from critical equipment such as the pump,
driver, controller, and so forth.
4.13.7.2 The pump room or pump house shall be provided
with a floor drain that will discharge to a frost-free location.

TBH, this isn't your problem. Mechanical or plumbing engineer should have provided a drain. But no doubt it's going to be a long argument.

Looks like mechanical engineer missed it.

Plan approval does not relieve any party to the code standards.

I have seen concrete floors be cut and excavated in order to install a standpipe drain.

Good luck!!!

Reply
Rusty Scott
2/8/2019 10:41:24 am

When you say main drain in the pump room, are you referring to a floor drain? I typically coordinate with plumbing to have a 3" or 4" floor drain especially when a BFP is in the pump room. Also typically fire pump test water is typically routed to an outside test header. That way water is discharged outside of the building. Some jurisdictions allow the test header to be located in the fire pump room and allow the use of hoses to be run out of the building.
If you're referring to the main drain off of the floor control assemblies, they are run to outside the building to drain to grade typically. NFPA 13-2013 8.16.2.1 & A.8.16.2.1 says all sprinkler pipe and fittings shall be installed so that the system can be drained. Which sounds like the basement pump room piping is not meeting that. If you only have the one pipe existing to the first floor a "drain 90" paired with globe valve can be used for draining the system (not testing). Sounds like if it's in a basement you could drain it to a bucket/trash can and carry the water out. (typically sprinkler installer move).

Hopefully this helps.

Reply
VINNY BOVES link
2/8/2019 07:44:33 pm

Hi Rusty,
When I say main drain, I refer to the requirement of the 2" main drain that is required anytime you use municipal water. The purpose of the main drain is to drain the sprinkler system when needed but most importantly to test the quality of the water supply. If the curb valve outside in the street is closed or closed by the water supplier and not completely reopened doing the required main drain test tells you either that there is a restriction in the pipe or that the curb valve is not opened all the way.
The closer the main drain is to the supply pipe the better and quicker you can get a reading. In the example I provide a fire pump in the "fire pump room" where the water supply enters the property from the street and no main drain was installed in the "fire pump room" which by the way is also where the backflow preventer is located.

Reply
Dewayne Martinez
7/11/2019 08:08:53 am

Wouldn't the yearly fire pump test also test the "quality" of the water supply?

Doug J
2/8/2019 07:40:20 pm

I think main drain is the wrong terminology. There needs to be a low point drains to get the excess water out of the pipe for repairs around the fire pump. Just because the plans being approved by the Ahj does not eliminate you from installing a code compliment system.

Reply
JAL
10/21/2020 12:18:15 pm

Related question:

What QUANTITY of water is usually expected at a fire pump floor drain/sink?

At the drain, I'm thinking my highest expected discharge water from the fire pump will be from casing relief valves (1 per pump).
There'll also be a low-point drain, and will also provide means of draining out a 60,000 gal tank.

Does anyone know where I find this information?
Fire Pump manufacturer Rep. maybe?

Reply
Landon "Wood Expert" Edgington link
1/12/2021 04:32:48 pm

This would be very useful for people that are just getting their new homes or even just planning to get one. Thanks for that!

Reply
Best Mortgage Brokers in Sydney link
5/14/2023 08:24:49 pm

Your blog post about placing fire pump in basement was exactly what I was looking for. Thank you for taking the time to share your knowledge with us. Keep up the amazing work!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT