We are upgrading protection for one of our Crude Oil Storage Facilities for a major oil and gas clients in the Middle East region. We have 4,000 gpm diesel driven pumps for fire water use. There are 8-inch pressure relief valves provided, per Section 4.20 of NFPA 20-2019. Section 4.20.4.1 (Type) reads as "pressure relief valves shall be either a listed spring-loaded or a pilot-operated diaphragm type." My interpretation of this section is that the listing is required in either of these cases, whether it's spring loaded or pilot operated. However, it's being challenged by those who are reading word-to-word meaning and saying that the listing requirement is only applicable for spring-loaded, and not for pilot operated relief valves as the sentence is separated by "or" along with the latter "a". If the letter "a" is not there, then I'm convinced with my interpretation that the listing is applicable for both cases. Also, I checked the handbook but it does not provided any further detail. Has anyone had any insight/experience as to whether the listed requirement applies to pilot-operated relief valves? I appreciate any further detail or discussions on the above with reference to code interpretations. Thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Alex
1/13/2022 07:27:20 am
Hi,
Reply
Mike L
1/13/2022 07:55:22 am
My 2 cents, section 4.20.1.1 states "Pressure relief valves shall be used only where specifically permitted by this standard".
Reply
Glenn Berger
1/13/2022 08:09:53 am
All products used in a fire protection system shall be listed. Code writers are not English teachers and this has been an issue at many instances.
Reply
Alex
1/13/2022 12:52:31 pm
English teacher... I barely speak English and its my primary language! Jokes aside, I agree. The code isn't perfect when it comes down to the fine print.
Reply
Sunil Kumar
1/13/2022 01:40:12 pm
Thanks for All responses. Got it.
Anthony
1/13/2022 08:17:01 am
The assembly as a whole has to be listed as well. As in the whole of the valve assembly not just individual parts.
Reply
Jesse
1/13/2022 08:17:16 am
With the exception of indicating valves on jockey sensing lines, absolutely everything on a fire protection system needs to be listed. In your case, you can use either a spring-loaded PRV or a pilot operated diaphragm type PRV, but in either case, they must be listed for use with fire protection.
Reply
SCHULMAN
1/13/2022 08:38:39 am
I wonder how "their" Insurance Agent would interpret it ?
Reply
Jay
1/13/2022 04:20:36 pm
In addition to the comments above, I recommend submitting a technical question to the nfpa. An NFPA 20 committee member will typically respond and may give you additional insight on intent or discussion that took place while developing the language.
Reply
Jon
1/14/2022 05:09:25 am
Many manufacturers are offering listed pilot operated relief valve. So that will not be hard to get...