According to NFPA 20, for any pump installation, the NPSH supplied must be at least equal to the NPSH required for the operating conditions specified.
So does the NPSHₐ need to be continuously maintained at or above the NPSHᵣ during pump operation? During the operation of the fire pump, the liquid level of the fire water tank will keep dropping, which may lead to a situation where the NPSHₐ is lower than the NPSHᵣ (unless the fire water tank is built at a very high elevation). Is this situation permitted? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Michael Newell
11/24/2025 08:26:42 am
There is an allowance in NFPA 20 to allow up to a -3psi when taking suction directly from a tank.
Reply
Cris
11/24/2025 06:47:48 pm
So is it acceptable that NPSHa < NPSHr due to the drop in water tank level during the pump's operation? Won't this cause cavitation in the pump?
Reply
Chad
11/24/2025 08:49:03 am
Mike's answer, to the point, spot on.
Reply
Dustin Tures
11/24/2025 09:50:44 am
Design your pump and tank system to provide the necessary pressure at the end of the required water supply duration. Ensure your pump rep understands the available tank head, suction losses, and available suction head at the pump flange at this time as well, and that it can be negative; some reps don't.
Reply
Jack G
11/24/2025 11:48:08 am
Npshr is a pump property. Its a minimum suction pressure to prevent pump cavitation .
Reply
Cris
11/24/2025 06:54:00 pm
Yes, it also indicates the required water level height in the water tank for the pump prior to operation.
Reply