I have a building that is changing from storage to a gymnasium.
Would the existing ESFR sprinklers be allowed to be used and spaced more than the 100 sqft? I have several sprinklers too far off walls in the existing placement. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
9/5/2025 06:16:47 am
I can be wrong about this as I'm not opening up a code book to double check but I'm pretty sure it's:
Reply
Glenn Berger
9/5/2025 08:16:46 am
You can keep the existing ESFR sprinklers but you must correct the issues with sprinkler placement.
Reply
Anthony Crispo
9/5/2025 09:11:31 am
I agree with Glenn here. Also I'd just be carful about intermixing lower k factor heads into the area. keep it as a standard set through out.
Reply
ANGIE KAMM
9/5/2025 08:19:30 am
We just had this scenario and ended up with so many over spaced ESFR Heads to walls (And were obsolete ESFR Heads) that we needed to swap out to 8.0K sprinklers.
Reply
Heather T
9/5/2025 08:28:39 am
When this type of scenario happens what flow and pressure does the ESFR require? Can they be used in a density area design approach?
Reply
Casey Milhorn
9/5/2025 08:30:04 am
You could possibly swap out to EC-25s and the spacing might be acceptable depending on how far off the wall they are placed. But you would need to make sure they are installed per their listing (spacing, deflector distances, hydraulic demand, etc.).
Reply
Dan Wilder
9/5/2025 09:18:46 am
Yes to use
Reply
Dennis Wilson
9/8/2025 09:03:12 am
Thanks Dan, so if I read this right, section 14.2.7.1.2 refers me to section 10.2.5. and this tells me that spacing per light hazard is acceptable and going more than 6' off walls is also acceptable. On another note, the Fire Marshal has approved using head guards, which are not allowed for ESFR sprinklers.
Reply
Jesse
9/5/2025 09:52:11 am
Agree with Dan - yes to use, no you can't change the spacing. The ESFR sprinklers are listed for their installed spacing. And you can use ESFR with OH and LH occupanices, but you can't increase the coverage.
Reply