For the protection of steel columns using sidewall sprinklers, what is the k-factor and temperature rating needed?
The existing upright sprinklers for the high-piled storage are 286°F. I couldn't find information for this in NFPA 13 2022. Any help or advice would be greatly appreciated. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Jon N
8/28/2025 08:38:47 am
This arrangement is likely an alternate method of protection to get out of fire-resistive-rated coatings on the steel structural members. As such, it is outside of the scope of NFPA 13.
Reply
Dan Wilder
8/28/2025 08:57:40 am
In the past, we have provided either the same temp or one temp level below, but not below 200°F. K-Factor is based on the discharge requirements being met (typically the surface areas being covered x Density) and I have used 5.6K & 8.0K sprinklers in the past.
Reply
Rich G
8/28/2025 09:56:39 am
Typically Column and Structural protection falls under NFPA 15, Orifice size can vary down to very small as your just protecting surface area of the column, but be wary any K-factor below 1/4" would require a strainer at your water supply. Temp if not an open head system would depend on your hazard and ambient temperatures.
Reply
Glenn Berger
8/28/2025 12:03:49 pm
My experience has been exactly what Dan stated above . Just add two sprinklers per column spraying into the web space.
Reply
Franck
8/28/2025 01:34:12 pm
You can also find some info in FM Global data sheet, such as maybe the one for turbines (for pedestal of lube oil tanks) in 7-101
Reply
Todd E Wyatt
8/29/2025 01:49:54 pm
The fire-resistance rating (FRR) of building elements (e.g. Columns & Beams) shall be determined by (1) of (3) methods as required by the scoping Code (e.g. IBC-2024):
Reply
Jack G
9/21/2025 11:15:51 am
I am assuming you are only talking about the columns that fall in the racks and not every column.
Reply