During a fire event, the pressure in a sprinkler system drops, and the jockey pump starts but cannot make up the pressure loss. Then, the electric fire pump kicks in.
Should the jockey still be running, or stop? Same for electric and diesel: should they operate together if the pressure still goes down and the electric pump cannot make the pressure up? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
9/18/2024 08:08:50 am
It really doesn't matter if it stays on or turns off. The On/Off points are above the starting pressure of the pump. While it may be available in the programming, having an additional low pressure Off point has not been a part of any of my Fire Pump designs thus far (Electric & Diesel, VSP & VFD, single/parallel/series Fire Pump setups with single or redundant Jockey Pump setups).
Reply
Chad
9/18/2024 08:08:54 am
It stays on. Its load is part of the electrical calcs. It doesnt affect system pressure (to any extent worth considering) when you have a true fire flow.
Reply
Anthony
9/18/2024 08:23:49 am
Doesn't matter as others have said.
Reply
Jesse
9/18/2024 11:43:31 am
Its going to keep running but it doesn't matter. I has no effect on the performance of teh system at that point
Reply
Mike
9/18/2024 12:06:07 pm
It will stay running.
Reply
Jack G
9/18/2024 05:07:55 pm
It should remain on but as described above it actually doesn’t matter.