Is it required by IBC or NFPA 13 to have a detached fire pump room or shelter to be protected by the sprinkler system as long as the fire pump serves the sprinkler protected building?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Brett
1/3/2025 07:06:04 am
It depends on the edition of NFPA 20 that applies, power source (electric versus diesel), and if the pump house is required to be sprinklered by the IBC for some other various reason not related to the fire pump like exposure protection.
Reply
Ahmad
7/12/2026 09:48:23 am
However, 2022 edition requires the "and" to add a sprinkler system, this and is for the diesel engine and the diesel tank. On the other hand, 2025 changes this "and" to "or"
Reply
Anthony
1/3/2025 07:15:29 am
The requirements come from NFPA 20 if the pump house is 50 ft away from the building it is protecting it does not require a sprinkler system for an electrical pump. NFPA 20-13 Table 4.12.1.1.2
Reply
Cris
10/23/2025 07:52:41 pm
So even if the distance between the pump room and the protected building is more than 15 meters, does the pump room still need to be equipped with an automatic sprinkler system
Reply
Jack G
1/3/2025 10:18:35 am
As I understand it, according to NFPA 20, in order for an installation to be considered “ fully sprinklered “, the fire pump building or room must also be protected. Ord-1 for electric pump, ex-2 for Diesel pump. . See 4.14.4 and I 4.14.1.1.2 and explained in A4.14.1.1.2. .
Reply
Jesse
1/3/2025 11:02:51 am
I hate answering a questions with. "it depends". But, alas it depends.
Reply
Todd E Wyatt
1/3/2025 04:21:43 pm
The scoping Code (e.g. IBC-2024) determines IF a building requires an Automatic Sprinkler System (ASPS) based on the Occupancy Classification(s) (OC) and/or other “Specific Building Areas and Hazards”.
Reply
Todd E Wyatt
1/3/2025 04:22:05 pm
REFERENCES
Reply
Todd E Wyatt
1/3/2025 04:23:43 pm
AHJs cannot "make" a Project provide an ASPS unless it is required by the adopted Codes.