NFPA 20 – Does the 10 pipe diameter suction requirement have to be one continuous straight run?
I’m looking for clarification on the NFPA 20 requirement for 10 pipe diameters of straight pipe on the suction side of a horizontal split‑case fire pump. NFSA’s Layout Book states: “The length of pipe that needs to be 10 pipe diameters long can be either vertical or horizontal, or some combination of the two, as long as there are no more elbows or tees with a horizontal change in direction in the length of pipe.” This makes sense—but when I look at NFPA 20’s own figures (specifically the “Right and Wrong Pump Suctions” illustration), one of the “Right” examples shows a 90° elbow dropping directly into a tee located right at the pump suction flange. In that configuration, there is no 10‑diameter straight run at all. My questions: Where in NFPA 20 is it actually stated that the 10 pipe diameters must be a single, continuous straight run of pipe? NFSA says the 10 diameters can be vertical, horizontal, or a combination, but NFPA 20’s figure seems to show exceptions. Is NFPA 20’s 10‑diameter rule only triggered by elbows/tees that introduce a horizontal component to the change in direction? (For example, a vertical elbow turning up does not trigger the 10D requirement.) Is this 10‑diameter rule only applicable to horizontal split‑case pumps? Or does it apply to all pump types? I’m trying to reconcile the NFSA explanation with NFPA 20’s figures and determine whether certain configurations truly require the 10D straight run. Thanks in advance for any clarification. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
2/23/2026 07:56:39 am
My way of visualizing this is if there is any water flow not perpendicular to the shaft of the engine/motor & impellor in a horizontal plane, that face of fitting for the change in direction is the 10 pipe diameters start point.
Reply
Maurice
2/23/2026 10:34:36 am
I like how you said "view it from the top" that really helps putting it into perspective. Thank you.
Reply
Brett
2/23/2026 08:01:01 am
"Where in NFPA 20 is it actually stated that the 10 pipe diameters must be a single, continuous straight run of pipe?"
Reply
Jack G
2/23/2026 11:32:02 am
There are sizes in a pump room that are governed by nfpa 20 and nfoa 13. The suction piping is sized for low flow to stop "bubbles" ( think of them as little explosions ) to prevent cavitation and increased wear and axial wear on the fire pump.
Reply