Is Large Circulation Space a 'Corridor' in NFPA 101?

2/13/2025

6 Comments

 
Subject: Two story convenience opening separation from corridors.

NFPA 101 (2021 edition) Section 8.6.9.1 permits convenience openings for two adjacent stories. But, these convenience openings shall be separated from corridors (requirement #3) and
further states that separation should be by a smoke partition (requirement #5).

How do you define a corridor versus an open floor area or lobby per NFPA 101, since no definitions are given within the code?

Jurisdiction is required to follow NFPA 1 and NFPA 101.

For example, a building has a large assembly space on the second floor. All doors from the assembly space lead to a ~40'-0" wide circulation space (+200'-0" long in the other direction). To reach the building exit stair, occupants from the assembly room must traverse the 40'-0" wide circulation space. Within this circulation space is a ~20'-0" x 40'-0" vertical opening that connects the 1st and 2nd floor.

Should this circulation space be considered a corridor
, and should the vertical opening be prohibited from being classified as a convenience opening without a smoke partition separating from the corridor?

Or is the 2nd floor space to be considered an open floor area, with exits immediately accessible in different directions (NFPA 101 7.5.1.1.1) and not consider it a corridor?

​The width of the circulation space seems too wide to be defined as a corridor but NFPA only provides minimum width requirements for corridors, and no maximum width for a space to be considered a corridor as far as I can determine.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments
Christopher Hallock
2/13/2025 08:47:11 am

NFPA 101 12.3.1(3) seems to permit this exact circumstance.

12.3.1 states:

"Any vertical opening shall be enclosed or protected in accordance with Section 8.6, unless otherwise permitted by one of the following:"

Then, 12.3.1(3) states:

"Assembly occupancies protected by an approved, supervised automatic sprinkler system in accordance with Section 9.7 shall be permitted to have unprotected vertical openings between any two adjacent floors, provided that such openings are separated from unprotected vertical openings serving other floors by a barrier complying with 8.6.5."

12.3.1(3) does not require separation from corridors and thus is "otherwise permitted".

This assumes that the occupancy classification is assembly.

Reply
Glenn Berger
2/13/2025 09:01:35 am

There is no code that can possibly define all "words" that are contain within its document.

Against my better judgement, this is one of those cases that I will utilize the definition from the IBC or even a dictionary. The IBC does define a corridor "as an enclosed exit access component that defines and provides a path of egress travel."

In your example who do not have an defined enclosure and as such the convenience opening is allowed.

Reply
JackG
2/13/2025 12:50:49 pm

In the 3 states/and large cities that I work in, the “ life safety codes “ are not” recognized as part of the code. ( sprinkler omissions )
NFPA 13 requires sprinklers with draft stops around those openings, if the convience is recognized as part of the egress. The wall / walls would require a fire rating.

Reply
Todd E Wyatt
2/14/2025 08:39:13 am

If a term (CORRIDOR) is not defined in the applicable Code, NFPA 101 Life Safety Code (LSC), then the “Merriam-Webster’s Collegiate Dictionary, 11th edition, shall be the source for the ordinarily accepted meaning” per LSC-2024 3.1.

Merriam-Webster’s Collegiate Dictionary
Corridor
noun
1 : a passageway (as in a hotel or office building) into which compartments or rooms open,
2 : a usually narrow passageway or route

This does not help differentiate IF this is a CORRIODR or not since the (2) “Convenience Opening” (CO) and the story’s Exit Access to the (2) Interior Exit Stairways (IES) both existing in this same area. This area could be interpreted to be a “LOBBY” versus a “CORRIDOR” which would NOT require it to be protected from the adjacent Assembly and Storage spaces.

If the LSC is the only applicable scoping Code for this project (e.g. no IBC), the first step in evaluating the compliance of this is to determine the OCCUPANCY CLASSIFICATION(S) (OC) of the portion of the stories that the CO occurs.

LSC-2024 includes the following suggested procedure for determining the Code requirements for a building or structure:

A.1.1
1) Determine the OCCUPANCY CLASSIFICATION by referring to the occupancy definitions in Chapter 6 and the occupancy Chapters 12 through 42. (See 6.1.14 for buildings with more than one use.)
2) Determine if the building or structure is new or existing. (See the definitions in Chapter 3.)
3) Determine the occupant load. (See 7.3.1.)
4) Determine the hazard of contents. (See Section 6.2.)
5) Refer to the APPLICABLE OCCUPANCY CHAPTER of the Code, Chapters 12 through 42. [See Chapters 1 through 4 and Chapters 6 through 11, as needed, for general information (such as definitions) or as directed by the occupancy chapter.]
6) Determine the OCCUPANCY SUBCLASSIFICATION OR SPECIAL USE CONDITION, if any, by referring to Chapters 16 and 17, day care occupancies; Chapters 18 and 19, health care occupancies; Chapters 22 and 23, detention and correctional occupancies; Chapters 28 and 29, hotels and dormitories; Chapters 32 and 33, residential board and care occupancies; Chapters 36 and 37, mercantile occupancies; and Chapter 40, industrial occupancies, which contain subclassifications or special use definitions.
7) Proceed through the applicable OCCUPANCY CHAPTER to verify compliance with each referenced section, subsection, paragraph, subparagraph, and referenced codes, standards, and other documents.
8) Where two or more requirements apply, refer to the OCCUPANCY CHAPTER, which GENERALLY TAKES PRECEDENCE over the base Chapters 1 through 4 and Chapters 6 through 11.
9) Where TWO OR MORE OCCUPANCY CHAPTERS APPLY, such as in a mixed occupancy (see 6.1.14), apply the MOST RESTRICTIVE requirements.

Some OCs (e.g. New Health Care - NHC) require that the “EXIT ACCESS CORRIDOR” (EAC) be separated from occupied rooms/spaces by partitions that “resist the passage of smoke”. NHCs also do not permit COs. This is why it is imperative to FIRST determine the OCs.

Reply
Todd E Wyatt
2/14/2025 08:46:07 am

Chances are, the IBC (e.g. IBC-2024) is the applicable Code. See the following for requirements for this “TWO-STORY OPENING” (TSO) :

IBC-2024
Chapter 7 Fire and Smoke Protection Features
Section 712 Vertical Openings
712.1.9 Two-Story Openings
In other than Groups I-2 and I-3, a vertical opening that is not used as one of the applications specified in this section shall be permitted if the opening complies with ALL of the following items:
1) Does not connect more than two stories.
2) Does not penetrate a horizontal assembly that separates fire areas or smoke barriers that separate smoke compartments.
3) Is not concealed within the construction of a wall or a floor/ceiling assembly.
4) Is not open to a corridor in Group I and R occupancies.
5) Is not open to a corridor on nonsprinklered floors.
6) Is separated from floor openings and air transfer openings serving other floors by construction conforming to required shaft enclosures.

Reply
Todd E Wyatt
2/15/2025 09:24:34 am

While the circulation space (to the left of the 2 storage rooms and the 2 assembly spaces) with the (2) two-story openings (TSO) and/or the (2) Convenience Openings (CO) could be argued that they do not meet the definition and/or intent of a "corridor", the passageway at the top of the upper storage leading to the top Interior Exit Stairway (IES) does meet the definition and/or intent of a "corridor" and should be separated from the TSO/CO.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT