Is Full-Size Water Meter Required on 6" Fire Line?

12/3/2025

8 Comments

 
I have a code official who is requiring a full-size water meter on the fire line preceding double check backflow.

The backflow has a 3/4" meter and
a small check on it with electronic connection capability for the water department. 

Are there any applicable code/standard references that mandate this?

A 6-inch meter on the fire line would run about $15k.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Brett
12/3/2025 06:29:54 am

When these are required it's typically a requirement from the local water purveyor.

Reply
Leroy
12/3/2025 09:06:56 am

We have a local purveyor that requires this, it's setup as a bypass near the tap. The purveyor provided a detail how they require it be installed.

Reply
Lawrence Stephens
12/3/2025 02:01:35 pm

Yes - never had a municipality require a meter on the fire line. We have the small backflow meter that detects that a leak is present, somebody stealing water, and usage during testing of sprinkler system (no pump). Clearly, not capable of registering a fully engaged fire sprinkler. We are getting the 360 deg two step, call water dept and see if they require a 6" meter on fire line who says call code dept, code dept says call water dept, when we tell them we did then call the water system contractor (maintains meters and what not) who says follow ordinance and the ordinance had no verbiage (as he sent me a copy) for a metered fire water line. So then he sent me to code dept who said call all those people. Called mayor who said call code dept - think I'll pull out my eyes and jump off a cliff. Thinking telling contractor to pay for tap and run to metered backflow (small bypass meter - 3/4") and tell them to tie it to their monitoring system.

Reply
Glenn Berger
12/3/2025 08:10:31 am

Providing a meter on the fire service would be a local jurisdiction requirement. The low flow bypass on a (double) detector check valve may not suit the local requirements. You will need to include the pressure drop across the meter and the additional shut-off valves in the hydraulic calculations.

Reply
Jack G
12/3/2025 05:45:57 pm

Maybe if the service has hydrants on it the water company worries about stealing water.( for an actual meter ).

Reply
Robert Morgan
12/3/2025 09:05:21 am

We (I as AHJ) have allowed a 4" F-2 meter on a 6" line with documentation from the manufacturer that the required flows and pressure will still be met. I would imagine that if the flows were high enough at some point you would need to worry about turbulence, but for the projects I dealt with this was not a concern.
NOTE: Illinois required fire and domestic lines to be combined into the building.

Reply
Casey Milhorn
12/3/2025 09:15:57 am

From my understanding, detectors on backflows can only meter water usage in small increments. Once the main checks on a backflow open up, most of the water usage will not be metered. A fire meter provides accurate metering at all flows. Then the question becomes why would a water purveyor require a fire meter to meter water usage at all, if we are only talking metering water usage during a fire event or annual testing (or more frequent if a fire pump is on your system). The revenue generated from this usage would take decades or more to recoup compared to the cost of the fire meter assembly. Of course, you could have a building owner using water from a downstream fire hydrant, or other source on the sprinkler system, but there are cheaper ways to ensure that doesn't happen than a fire meter. Again, from my understanding talking to water purveyors, it's more about them being held accountable by the state department of conservation, which I assume has federal pressure on them. Chlorinated/treated water must be accounted for due to a variety of reasons. The purveyor can actually be fined, or face other consequences for X amount of unaccounted for water usage. It's easier, in some water districts, to just ask the building owner to pick up the cost of a $20k to $60k fire meter assembly than deal with DEC. From my experience, this is a lot more common in more affluent areas where owners can afford the cost. It is sad to see that sometimes this extra cost will kill a small project, like a community center, church, daycare, etc. It also costs us taxpayers when fire meters are required on tax funded projects.

Reply
Jack G
12/3/2025 05:11:38 pm

Some water companies require the same size meter as the tap and service and there is usually a monthly charge.
Some do not and the owners weight the cost differential and weigh the cost of oversizing other components to make up for the additional friction losses .
My last example was an owner that had his plant protege with mains hydrant pump , meter pit, wet tap.
The system was installed and never worked. Problem being a 100 ft elevation difference in tap and test and another 23 feet to pump. 8 inch tap 6 inch meter 8 inch BFP, 8 inch mains 1500 gpm pump ESFR sprinklers, 40% installed improperly, Chubb insurance. ( I thought I knew a lot about ESFR until I met this insurance company rep ).
The owner was a hunter. He had 3 major companies come in and couldn’t fix it. He indicated there was a plack on his wall next to a tiger that was for the next failed sprinkler contractor. lol. Guy was tough but great )
Bottom line— underground too small ( meter price difference was 2000 a month so untouchable ) needed a smaller pump ( 1500 overflowed the water test ) and a couple hundred ESFR s moved.
So I prepared docs and calculations, offered a 1000 gpm pump flowing 140% in calcs ) ( 1250 was too big also)
Ran new 12 inch fiberglass underground to the new pump, tied old 8 inch to it in the pump room) ( leaving 8 main be ).
Did a final acceptance test flowing the 250 hose outside the pump room at the same time as new pump test.
Had a 22 psi safety, my calcs showed a 21.5 psi safety.
Chubb accepted. He “ then” wrote a check to me.( after doing calculations at each phase )
So point to make —- changing to a smaller meter, if the flow thru it satisfies the demand — saves Bukuu bucks monthly— and the water company accepts it, and AHJ — then go ahead and do it.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT