|
I ran into this issue today with a cage installed in close proximity to an upright fire sprinkler.
Is this an obstruction to the sprinkler? It's open wire mesh from the head to the floor; the only obstruction is the top angle near the sprinkler. The deflector is higher than the beam; it appears there would be very little obstruction to the development of the spray pattern overall. Facility has an open concrete ceiling. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
6/12/2026 07:50:40 am
Yes.
Reply
Dan Wilder
6/12/2026 08:05:24 am
I'm just looking at the bricks beyond and counting (old school measuring)...assuming the standard 8x8x16 CMU that sprinkler looks to exceed the 22" max below deck...again assuming obstructed construction just out of frame within the 1" to 6" above the deflector...
Reply
Chris
6/12/2026 08:24:32 am
Food for thought, why didn't they run the pipe directly over the cage?
Reply
Glenn Berger
6/12/2026 08:49:18 am
The sprinkler shown in the phot does not appear to be currently in compliance with NFPA 13. Would recommend a complete review of existing conditions.
Reply
Anthony Brown
6/12/2026 01:34:54 pm
Yes, on several points. As already pointed out, it appears that the deflector doesn't meet distance below ceiling requirements, also, the flow exits in a slight downward direction and from the picture there will be impediment to flow and distribution. Install a candlestick and move on to the next issue. because if there is this one, I'm sure there are others as well
Reply
Jack G
6/12/2026 03:56:17 pm
As pointed out above, it is not in compliance with code.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2026
PE PREP SERIES |
RSS Feed
