I have an older class B Mercantile space that is sprinklered but not alarmed. The last tenant was a large pharmacy chain that monitored their own fire alarm or sprinkler systems. When they left they removed the alarm panel.
The tamper and flow switches are still there, as well as an exterior electronic flow bell. Does this sprinkler system require electronic monitoring? Currently they have nothing monitored. I would like it to be monitored, but need something to back me up. We adopted the 2021 I-Codes and 2015 NFPA 101 (Statewide). Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Glenn Berger
8/27/2024 08:07:24 am
The requirement for "electronic monitoring" would come from the AHJ, insurance, locality needs.
Reply
Pete H
8/27/2024 08:13:12 am
When you say "exterior electronic flow bell" is this an electric bell or is this a pneumatic water motor gong on the outside?
Reply
David Kendrick
8/27/2024 08:23:49 am
Pete, what is a “pneumatic” water motor?
Reply
Pete H
8/27/2024 08:38:54 am
Hydraulic is correct.
Franck
8/27/2024 08:26:41 am
As indicated by Glenn, the requirement will normally come from the AHJ or any otrher specific request/regmlementation.
Reply
Sean H
8/27/2024 08:51:10 am
I believe your journey could start in Chapter 9 of the IBC.
Reply
Jack G
8/27/2024 09:22:42 am
Sean has it.
Reply
Todd E Wyatt
8/27/2024 09:23:50 am
Your initial review should start with the scoping Code (e.g. IBC-YYYY?) that was applicable/adopted when the building’s Drawings were initially reviewed by the AHJ.
Reply
Randy Kimbro
8/27/2024 11:32:48 am
As an AHJ, sprinkler MUST be electrically supervised ...
Reply
Jesse
8/27/2024 12:05:06 pm
While it's AHJ driven, the short answer is yes. They'll need a riser monitoring panel.
Reply
Conrad
8/27/2024 01:37:22 pm
In my NFPA jurisdiction, I have seen similar where either fire alarm or electronic supervision for fire sprinkler was removed by the tenant when they left without permission of the AHJ. NFPA model code requires a permit for the modification or removal of a fire protection system.