Would you consider this (Easy Up canopy) an obstruction that can be written up during an NFPA 25 annual inspection?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
12/23/2025 06:23:06 am
Not unless it's bolted to the floor.
Reply
12/23/2025 07:35:43 am
Not within the 25 report. It is not within the clearance requirements as defined in Section 5.2 of NFPA 25. 25 does not look at obstructions like this. If it were missing an escutcheon, was loaded, installed in the wrong orientation, was leaking, or a select few other things it would fall under the Scope of 25 for a write up.
Reply
Dave
12/23/2025 08:26:28 am
The question is about violating NFPA 25 for the purpose of ITM standards. But from an AHJ perspective, who does annual fire and life safety inspections based upon IFC and NFPA 13 standards, this would be a violation, correct?
Reply
Jesse
12/23/2025 08:30:25 am
While that's a pretty dumb idea, its not permanently installed so it falls under temporary office furniture.
Reply
Glenn Berger
12/23/2025 08:36:56 am
Would this situation be written-up? NO.
Reply
Anthony
12/23/2025 10:07:21 am
Agreed - No.
Reply
Jack G
12/23/2025 09:28:11 am
I m with Jessie. It looks like a “:display “ that will be there for a while like an exhibition in a conference center.
Reply
Jack G
12/23/2025 09:35:42 am
A loophole for the tent might be that there appears to be “ no sprinklers above the canopy” so it may be a “ non sprinklered building” or spray that would be blocked.
Reply
Jack G
12/23/2025 09:40:58 am
So if the building is protected by sprinklers, and the walls and ceiling was built as part of the display ( but not sprinklered) then the display room, requires sprinklers, and the tent removed.
OP
12/23/2025 10:12:01 am
The building is fully sprinklered.
Chad
12/23/2025 11:29:55 am
This is not a 25 issue. It is a fire code enforcement issue.