Under NFPA 13, 2019 Edition, does Section 8.2.3.1 provide the option of using 8.2.3.2, 8.2.3.3, 8.2.3.4, 8.2.3.5 or 8.2.3.7 to size the system?
Could I size an 800-gallon EH1 dry system to deliver water to a single test connection in 60 seconds based on 8.2.3.2, or must the system be calculated for water delivery by a recognized program per 8.2.3.5 and provide a 4-outlet test manifold with a 45-second time limit? Is the manifold just an option? I've been confused on this for awhile...thanks in advance!! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
Dan Wilder
6/4/2026 08:57:23 am
In your example, the system exceeds 750 gallons and would need to comply with the water delivery requirements of 8.2.3.6.1 with the manifold and 45 sec delivery time however, this can be done via a field test instead of water delivery time calculations per 8.2.3.7.5. Now, failing that test after the system is installed would be extremely impactful with a potential for a lot of rework so getting the calculations completed first is a better option.
Reply
jason
6/4/2026 12:11:00 pm
Hi Dan,
Reply