Can any installers or maintainers provide insights into automatic air vents in fire sprinkler systems?
In your experience, do these vents ever leak water while operating? Trying to understand why specifications often require these vents to be piped to the exterior. Although manufacturers claim that only air is released, I’m curious if they occasionally sputter or drip water and whether this has caused maintenance issues. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
8/26/2024 06:47:57 am
I can answer why specs ask for these to be piped to a "wet ok" area. Generally I'll have these vents located or piped to a janitors closet so when you're purging the air from the system you can allow for some flow of water as more air settles out of the system, similar to a flushing exercise. Also there is nothing an owner hates more than a sprinkler system they didn't want in the first place leaking adding a headache to their lives.
Reply
Anthony
8/26/2024 08:19:44 am
I'd also add that manufactures claim a lot of things that end up with dubious results "in the field".
Reply
JI
8/26/2024 08:09:00 am
Potter has an air vent with a drip pan for water to gather in:
Reply
8/26/2024 08:20:23 am
Code does not require the air vent to be piped to the exterior or additional drainage line be added to the vent outlet. There is going to be water molecules in the vented air so you should not locate the vent so that exhausting air blows directly onto a beam or wall where they can accumulate. Installation orientation by the contractor and internal float design which varies by MFG may also impact potential leakage. For more information I recommend visiting www.purgenvent.com
Reply
Dan Wilder
8/26/2024 08:21:33 am
There is some moisture that passes by the float valve and can drip (it's a basic mechanical lever & float...air enters, float drops opening the air vent port at the top, float rises as air is expended, air vent port is closed....repeat for new air entering the assembly). It's not a lot but over time can be like any other leak that creates discoloration and damage on whatever is beneath.
Reply
Franck
8/26/2024 09:26:13 am
As indicated above, in normal conditions, there is no "real" water leakage, but mostly moisture being released.
Reply
Dave
8/26/2024 12:17:25 pm
1. Code does not “require” an automatic air vent to be piped to drain. That decision is left to the designer.
Reply
Dave
8/26/2024 12:18:40 pm
^^ The comment above was meant to be prefaced by:
Reply
Jack G
8/26/2024 03:06:27 pm
Great responses all true.
Reply
chris
9/4/2024 11:47:15 am
Nobody would have this problem if we still piped the inspectors test at the furthest point of the system and got rid of test and drains.
Reply
9/4/2024 12:30:38 pm
Chris,
Reply