MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Include Exhaust Sprinklers in Paint Booth Calc?

4/25/2025

10 Comments

 
NFPA 33, 2018 Section 9.6.2.1 reads "The sprinkler design area shall not be required to exceed the area of the booth or room in which spraying or resin application is conducted."

My project has a large downdraft paint booth for buses. There are two concrete pits (4-ft height, 3-ft width, 80-ft long) beneath the paint booth that are covered by open grate flooring.

(1) Does the above reference mean that the exhaust duct sprinklers do not need to be included in the booth hydraulic calculation?

I have a large paint booth, and it has 4 exhaust ducts.

(2) Is sprinkler protection required within the pit?

Do these heads have to be included in the booth calculation or can they be considered heads under obstruction?

If sprinkler protection was within the pit, the bags had to be regularly changed, which creates an issue for the end user and adds a large demand to the calculations. I think it would be unlikely that the sprinklers would operate in the concrete pit, as the overhead system should adequately protect the booth itself.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Glenn Berger
4/25/2025 08:46:21 am

- Sprinklers within the Pit -- Yes they are required. Without more specific details of the interface between the paint booth and the pit, I cannot provide a proper response to the inclusion in the hydraulic calculations question.

- My experience with paint booth exhaust systems is that the duct is an extension of the booth itself. Most likely the sprinklers in the exhaust duct will need to be included in your calculations.

Reply
Colin link
4/25/2025 10:57:27 am

I'm also very curious what the consensus is here. I recently completed the shop drawing design for a large military pain spray booth. For my project, I calculated the booth separately from the duct based on this:

9.5.1.2.1 - The sprinkler design area shall not be required to exceed the area of the booth or room in which spraying or resin application is conducted.

And I calculated the exhaust duct separately per this section:

9.5.1.6* Duct Protection. (6)*The system demand shall include the discharge from the hydraulically most remote adjacent sprinklers in a common 30.5 m (100 linear ft) area of duct (horizontal and/or vertical).

There is NO WAY the water supply the gave me will support both the spray booth and the exhaust duct calculated together. But this annex material has me worried:

A.9.5.1.6 Water supply requirements for most industrial paint spray operations should be adequate to supply all automatic sprinklers in the spray area. Loss experience has shown that fires starting in the exhaust duct can spread to the spray booth and that fires starting in the booth can spread to the exhaust duct.

The project is currently under review, so I'll see how it goes, but not sure what my course of action will be if they ask for booth and duct to be included in the same calculation.




Reply
Jack G
4/25/2025 11:49:37 am

It has been my experience that the booth , the area in the floor , and filters , also exhaust ducts will require sprinklers. ( in the hydraulic calcs )
If the water supply is a problem, ask for clarification. I ve had AHJ s only ask for sprinklers up to the filters be calculated, and exhaust ducts separate, their reasoning , I think , is the filters would contain the fire to the booth.
What did the A&E show, or denote ?
Maybe a change order ?

Reply
Colin link
4/25/2025 12:08:51 pm

Yes, that's been my past experience too. However, in this case, either the EOR didn't include exhaust sprinkler with the booth in their BOD calculations, or the EOR messed up on their hydraulic calcs. And without express direction from either NFPA 33 or the A&E plans, my quickest route to find out what really happened is to submit a design that the water supply is capable of handling, which in this case is a separate calc for booth and exhaust, meets the requirements of NFPA 33 (which doesn't expressly say to include both booth and exhaust together), and see what they say. If they accept it, then we're good. If they don't, they'll have egg on their face for proposing a system design in the A&E documents with an inadequate water supply, and they'll have to fix it on their end, with a substantial change order likely. Will keep this thread posted on the result.

Reply
Brett
4/25/2025 01:07:25 pm

In my opinion section 9.6.2.1 is there to clarify that you don't need to calculate the booth in combination with the ceiling level sprinklers above the booth.

Section 9.6.3 - "The water supply shall be sufficient to supply all sprinklers likely to open in any one fire incident without depleting the available water for use in hose streams."

9.6.3 doesn't explicitly say to include the ductwork in the calculations, but the annex does support that idea as mentioned above by Colin. In most cases I think that the ductwork should be included in the calculation unless there is some sort of separation put in place that will stop fire in the booth from spreading to the ductwork or vice versa.

Reply
Jay
4/26/2025 11:18:33 am

See the definition of Spay Area in NFPA 33. Yes, sprinklers are required in all those portions of the spray booth that are included in the definition of Spary Area, and they are all included in the calculation.
Couple interpretations from NFSA and AFSA to note from my recent experience with this:
You are not required to add phantom flow to the EH2 booth calculation because the standard species the design area is only the booth.
The intake/makeup air duct does not require protection because it is specifically excluded in the definition of Spray Area.

Reply
Colin link
4/28/2025 11:07:18 am

UPDATE: I just got the review back on my above mentioned DOD spray project. The EOR approved my hydraulic calculations and is NOT requiring us to calculate the booth sprinklers and the exhaust sprinklers at the same time. So, much like the wording in NFPA 33, it appears this is not a simple cut and dried situation, with an easy 'YES' or 'NO' answer. The FPE reviewing my plans for this project has over 40-years of experience in every aspect of fire protection and specializes in DOD work, and special hazard applications, so it's not a matter of the reviewer overlooking or missing an obvious error. The booths they're using may have some prevention means for fires spreading into the ducts, such as dampers, but I don't have much info on the booth design. Anyway, I got the answer I was hoping for. I'm hoping this

Reply
robb k
4/30/2025 08:12:52 pm

I have had The DFPE rule the other way... The problem with the his remarks required us to include the calc... and include a 11k factor head per UFC tabbles for EH1 whereas the NFPA only required 8k - the head was 17 ft higher than the design area - and that was also the most remote - it totally canned the project becuase our scope could was required to use an existing pump - due to this ruling itfailed to provide the flow and pressure - due to this one head driving the calcs way above the existing capabilty of the 750gpm pump... i tried to argue that this is not a design area sprinkler, as well as an 11k head in a 30inch round duct was sever overkll (flooding the duct) - the area density being completely carried over into a duct fell on deaf ears.

Reply
robbk
4/30/2025 08:17:23 pm

oops ufc table for extra hazard was 11k, NFPA 33 for in-duct was 8k

Chris
4/29/2025 12:40:54 pm

Adjacent topic, work with your structural engineer to ensure that the ducting can handle the pooling water in the ducts.

In my experience with DOD paint booths, I did not include the flow of the ducts, just the spray area itself.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT