In Rack UPS Under 20 kWh Considered an ESS?

7/9/2026

11 Comments

 
I have a project I'm working on for a data center, and the owner is requesting a Hazard Mitigation Analysis (based on NFPA 855). I'm trying to see if NFPA 855 is applicable since it relates to energy storage systems (ESS).

The end user will have a UPS installed in each rack instead of a central UPS, and each rack will only be 0.55 kWh.

FM is also applicable in this case, but FMDS 5-32, Section 2.3.1.4.2 indicates that if your in-rack UPS exceeds 20 kWh, then that pushes the system into an ESS and FMDS 5-33.

But, NFPA 855 indicates that if aggregate quantities within the fire area exceed 20 kWh (which we would be for the data hall), then it's defined as an ESS.

Is the in-rack UPSs below 20 kWh are actually defined as an ESS or if they're just information technology equipment and NFPA 855 doesn't apply?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Joe Mc
7/9/2026 08:48:00 am

IFC 2024 section 1207 and related sub section will mostly govern,
if the AHJ is on an older edition i would still use the 2024 edition for liability issues.

https://codes.iccsafe.org/content/IFC2024V2.1/chapter-12-energy-systems#IFC2024V2.1_Pt03_Ch12_Sec1207

Reply
Jack G
7/9/2026 08:53:25 am

Per NFPA an ESS is an energy storage system. It stores energy and releases it later. That usually means lithium ion batteries. These batteries stack together in large racks for hones or businesses.
Some of the rules:
Use standard automatic fire sprinklers and may need a dry system for outdoor units.
System must spray a minimum 3 density over the entire battery area.
Goal is to prevent the fire from rack to rack
All ESS designs must follow NFPA 855.
Yhink of a battery as a hot charcoal grill.Too much heat to blow up. Water soaks the batteries to cool them down fast. This stops the " thermal runnaway."
Nfpa 855 is the primary protection standard for ESS storage. It mandates system listing's to UL 9540, Establishes spacing and ventilation rules, requires fire suppression, and requires site specific HMA, to prevent cascading thermal runaway.
Water is the most effective cooling agent.
TRPP ( thermal runaway prevention) must feature to absorb heat and stop propagation to other cells.
Fire detection systems such as off gas thermal image or radiant energy detectors must incorporated.
For systems exceeding certain energy thresholds, 600 kwh, explosion control and dedicated exhaust ventilation are mandatory
Owners must submit an ERP to the AHJ. Energy planning and response plan.
Nfpa 855 does apply.

Reply
Michael Knott
7/9/2026 12:15:12 pm

Appreciate it!

Reply
Jocelyn
7/9/2026 08:59:13 am

FMDS 5-32, the IFC, and NFPA 855 all scope their documents a little differently. I agree with your assessment of FMDS 5-32. The IFC also doesn't specify aggregate capacities for Section 1207 applicability, so I would argue Section 1207 doesn't apply to this case either.

But since you are being asked to comply with NFPA 855, the application Table in the Scoping Section 1.3 requires that the standard apply to an aggregate capacity of over 20 kWh per fire area. So although each individual in-rack ESS is less than 20 kWh, in aggregate for the fire area, they exceed 20 kWh, and yes NFPA 855 applies.

Reply
Michael Knott
7/9/2026 12:13:53 pm

Thanks! If you're the same Jocelyn in the MeyerFire University series on ESS, thank you very much! I started watching those as I was banging my head against the wall and it helped to clear some things up.

Reply
Jocelyn
7/9/2026 12:31:06 pm

It's me!

Dan Wilder
7/9/2026 09:03:48 am

I have seen this on a couple DC's lately and even with the dispersion or individual ESS components (ITE and the separate ESS components), the aggregate total within area drives the overall design. The designs have been able to utilize information specific to testing results that were provided to the AHJ by the owner as allowed in IFC 1207 for density, area, and configuration requirements and they were allowed to go with a lesser density however the area remained + applicable increases like dry/preaction, air velocity limits...

Between the IFC 1207 & NFPA 75, 800 (new in creation), and 855 they are all trying to keep up with and better define the equipment, hazards, and protection schemes. Try to always use the most current even if the AHJ hasn't adopted it.

As I sit on and/or will possible be accepted into the above referenced NFPA's, the above is my sole opinion and not a representation of any NFPA standard or committee nor a formal or informal interpretation....or something like that.

Reply
Michael Knott
7/9/2026 12:11:12 pm

Thanks!

Reply
Ricardo Gonzales
7/13/2026 01:02:11 pm

You should also check with the Owner and see IF they've done full scale testing. That would and should be listed and identified in an HMA which would allow limited sprinkler and detection schemes.

Reply
Raymond Armas
7/15/2026 04:55:14 pm

I believe the Threshold Quantities in table 1207.1.3 is based on the aggregate energy capacity of all ESS in the fire area. Section 1201.3 provides insight to this measurement concept for the Maximum Allowable Quantity threshold in Table 1207.5. I would have to assume the use of aggregate capacity would be the same in establishing the applicability of Threshold Quantities.

Additionally, NFPA 855 applies to energy storage system (ESS) installations that exceed the aggregate capacity values shown in Table 1.3, in each fire area or outdoor installation. The table is titled "Threshold Levels per Each Fire Area or Outdoor Installation," and it establishes thresholds based on the total (aggregate) amount of energy storage present in that area or installation, not individual rack or unit capacity.

Hope this helps.

Reply
Jocelyn
7/15/2026 05:56:30 pm

I don't agree with that interpretation of IFC Section 1201.3. The section header is for "Mixed system installation" and the section considers the aggregate sum of all ESS types (PV, Fuel Cell, electrochemical ESS) with regards to their respective MAQs, in the event that multiple types of ESS are in the same fire area.

This is akin to Section 1207.5.2.1, which is also in regards to mixed electrochemical energy systems. The word "aggregate" in this section is in reference to the sum of the percentages of each electrochemical ESS type divided by its respective MAQ.

This is supported by the commentary for these sections.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT