We are protecting a single row storage rack that is located beside a wall. The distance between the face of the storage rack and the wall is approximately 18". We are installing in rack sprinklers.
Can the line of in-rack sprinklers be installed along the face of the single row rack, between the storage rack and the wall? Or must the line of in-rack sprinklers be located inside the storage rack? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Jesse
5/7/2025 08:35:08 am
Face sprinklers are generally used differently than in-rack sprinklers (IRAS). It really depends upon your design criteria.
Reply
franck
5/7/2025 09:39:40 am
I think the question is not for face sprinklers but for the “longitudinal flue” sprinklers.
Reply
Chris N
5/7/2025 08:39:09 am
In-racks are the bane of my existence (Team ESFR here). My three cents is that would you want something to come by and hit and have an activation? In racks and longitudinal and latitudinal flues are spaced to protect the system just as much as the commodity.
Reply
franck
5/7/2025 09:38:10 am
I am team ESFR as well for new installations, but in existing situations, if you don’t want to replace all ceiling’ s sprinklers (and possibly the water supply), in rack is the less expensive solution
Reply
Jack G
5/7/2025 08:53:28 am
If the distance between the rack and the wall is 2 feet or less, yes the row of sprinklers can be spaced outside the rack as if it were a loungitudinal flue snd the spacing between sprinklers would be like its a double row rack.
Reply
Jack G
5/7/2025 09:13:30 am
For a client i ve installed them on a wall bracket on the wall 6 inches off the rack like its a 12 inch flue space. Client worried about fork lift drivers.
Reply
Jack G
5/7/2025 09:17:40 am
In my opinion, face sprinkler applications do not apply here as the description of the application is best described as flue sprinklers, flu space formed between the rack and the wall.
Franck
5/7/2025 09:35:57 am
Fully agree with Jack (I also grown up with 231 and 231c) and it was still the case within NFPA 13 (with appropriate sketches for in rack sprinklers (iras) and single row racks - srr) until one of the last editions (can’t remember if it was 2019, 2022 or 2025).
Reply
Jack G
5/7/2025 09:41:30 am
Also for a client we ran the sprinkler line high in the joist, dropped down between the rack and the wall, used a split ring double nuts and washers,to attach the drop from the above line to the rack. We felt this was easier then running ( labor) in the rack to run the line.
Reply