When calculating overhead systems with in-rack sprinklers, how much in-rack demand is added to the calculations?
I assume all in-racks within the most remote area, but want to ask to be sure I'm getting this right. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
10/3/2025 06:05:20 am
All the in-rack sprinklers in the design area typically unless you're using some exception due to circumstances of storage in the code.
Reply
Brett
10/3/2025 06:42:14 am
The answer is it depends. It depends on the sprinkler type, commodity being protected, storage height, open shelves or solid shelves, and how many rows of in-racks are being provided. If this is an NFPA 13 question and not an FM or NFPA 30 question, then the specific section depends on which edition of NFPA 13 is applicable. If you're in the 2019 edition then look at section 25.12.
Reply
Anthony
10/3/2025 07:33:36 am
As other have said: "it depends" which I would totally understand is not as helpful as you'd like.
Reply
Dan Wilder
10/3/2025 08:04:27 am
Careful with this...hydraulically remote vs physically remote are not always the same location, especially with different piping configurations for overhead vs in-rack layouts.
Reply
Adam
10/3/2025 08:23:04 am
I remember doing an in-rack design where the most demanding racking was not located under the most demanding ceiling area.
Reply
Glenn Berger
10/3/2025 08:21:14 am
You got some really good responses to your question.
Reply
Franck
10/3/2025 09:40:00 am
You have to add the number of IRAS based on the commodity classification and number of level of IRAS.