I have a situation where I have cold storage warehouse 20k sq. ft. The entire facility is cold storage.
This issue is that some folks believe that if the occupant reduces the rack storage to below 12', then the entire place can be classified as miscellaneous storage. Which, I know, is not correct due to the definition of miscellaneous storage. Please weigh in on this to either support my thought or tell me why I am incorrect. But where does palletized storage placed in solid piles come into play? Where is the information that says that solid piles (palletized on ground storage) are limited to a certain size? Height? Most importantly, the aisle spacing is my main question. I see back-to-back palletized storage with no aisles at all. Like 10 pallets deep, 3 high, and 6 pallets wide. I looked in NFPA 1 and 13. I don't want to come at this from a life safety standpoint, but rather from a sprinkler protection standpoint. Commodity class is 3. Fresh fruit in cardboard boxes. Thank you to this community! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
10/29/2026 07:25:21 am
Well, you already pointed out this doesn't fit the definition of miscellaneous storage.
Reply
Dan Wilder
10/29/2026 07:57:10 am
Easiest way I know to put a classification on this....
Reply
Jesse
10/29/2026 08:25:57 am
While it isn't misc. storage, I would consider it low-piled storage. It didn't identify a commodity class, but presuming Class-III, an overall OH2 density would govern.
Reply
Streeter
10/29/2026 11:26:51 am
Others has covered the sprinkler requirements but for aisle width take a look at 1018 of the IFC. (If it dips into high-piled, which i don't think is the case, it would be in 3206.10 of the IFC.)
Reply
Jack G
10/29/2026 01:23:22 pm
Agree with above.
Reply