MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Hydrostatic Test Req'd for Adding Few Sprinklers?

12/2/2024

14 Comments

 
Is a hydrostatic test required for adding two new sprinklers to an existing system?

For this, assume it can be isolated, and the local jurisdiction refers to NFPA 13 - 2016 Edition.

This is the most referenced code outside of the obstruction rule, and is the most common I've seen interpreted differently amongst professionals.

Reference Chapter 25, Section 25.2. What is your "threshold" for triggering a hydrostatic test?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Dan Wilder
12/2/2024 07:25:50 am

Technically, yes on all systems per 25.2.1.4 (working pressure) and again 25.2.1.4.1 (200 PSI for modifications >20 sprinklers) or when isolation is not possible, test to working pressure per 25.2.1.4.2. So, no matter what, there is a test. I think the issue is everyone jumps to 200# (up to 225#) when they hear "Hydrostatic", not just a given pressure for a set amount of time as defined in 3.8.1.14.3.

The 2019 Edition moved this into its own Chapter 29 for "Existing System Modifications" (specifically 29.7) and does not fall into Chapter 28 for System Acceptance.

However, many AHJ's have modified this to their liking. Some of my AHJ's do not require testing when the work is 20 sprinklers or less (or they just want the system locked in at working pressure so technically a "working pressure" test), some like to see 50 PSI over working (kind of picking and choosing), another one used to state 20 sprinklers/40 fittings/40 feet of pipe (exceed any of those 3 and a 200# hydrostatic test needs to be performed), and others that have hardlines hydrostatic testing on all modifications that need to go to 200 PSI (we will typically isolate the area of work or get a letter signed from the owner about areas outside our scope becoming issues).

Reply
OP
12/2/2024 07:10:22 pm

Thanks for the response. I take a very similar stance as you. Also, thank you for pointing to a seemingly simple but very helpful reference to the definition.

Reply
Anthony
12/2/2024 07:37:28 am

Yo can always get the base of riser pressures and flow, At least the start of a curve. You'll have a static pressure at the riser and a residual pressure when you flow through the test port on the system. Use the test port and K factor and calculate the flow given the pressure on the riser. Note this should only be done where the test port is on the riser not a remote test port.

I'd think that would suffice for a 2 head addition and not need calcs all the way back out to the street.

Reply
Glenn Berger
12/2/2024 08:13:11 am

I have never had a project that a hydro test was not mandated. Normally just at system pressure for any type of system modifications regardless of the number of sprinklers added or subtracted.

Reply
OP
12/2/2024 07:13:10 pm

Thanks for your response. I believe, like Dan noted really well above, is that people tend to jump to a definition of hydrostatic testing automatically triggering a 200 lb. test and not other methods i.e. system pressure, 50 psi above operating pressure, etc.

Reply
Anthony P
12/2/2024 08:17:36 am

As Dan said, confirm with the AHJ. New York has a few different scenarios for this. Whether its Port Authority or DOB. I have seen it where the AHJ just wanted an Air Test and for it to not lose pressure.

I have also seen some scenarios where it was stated once you touch the system you own it so be very specific on the matter.

Reply
Jerry Clark link
12/2/2024 09:50:10 am

And to back up what Dan said at the beginning of the thread, the 2016 commentary recognizes that systems may not require a full hydrostatic test for minor modifications:

"Paragraphs 25.2.1.4 and 25.2.1.5 address additions and modifications and specify when new piping installations are to be isolated and tested. In many cases, segregating new work from existing work is difficult. To require the entire system to undergo another hydrostatic test when only relatively minor changes are made is unreasonable and not required by NFPA 13.

Where system modifications are made and the piping cannot be isolated, such as relocated drops, NFPA 13 provides some flexibility and permits hydrostatic tests to be conducted at the system’s normal static pressure. In general, existing portions of the system do not need to be subjected to a new hydrostatic test."

Reply
Anonymous
12/2/2024 07:21:04 pm

would you consider two new sprinkler heads to an existing system, a "modification"?

Reply
Jack G
12/2/2024 10:17:09 am

I agree with Jerry.
I usually ,in my proposals , do not include a hydro of the entire system at 200 psi. Just the 50 psi over the static as stated in nfpa 13.
I also state in acceptance of proposal that if the 200 psi hydro is required, ( and the hydro of 50 psi over the system pressure) my company is not responsible for fixing the leaks or water damage and will be addressed as a T&M change order.
This is usually the practice in the 3 states I work in and is generally an accepted clause to contract.

Reply
Ryan
12/2/2024 11:55:24 am

Where are you getting the additional 50psi over system pressure?

Reply
OP
12/2/2024 07:16:54 pm

NFPA 13 - 2016
25.2.1.2

Ryan
12/3/2024 12:07:07 pm

The 50 psi is only when the system pressure is always at or higher than 150. So if static on system is 160, it has to be tested at 210. No other time do you have to add 50 pounds.

Reply
sean
12/2/2024 10:18:48 pm

all new heads need it. modifications can can be at system pressure.

I think the isolated is abused. being isolated does not need to be easy just possible.

Reply
Mark Harris
12/8/2024 11:43:21 am

Agree that sometimes the requirements seem excessive. I always thought the 20 sprinklers was reasonable compromise. If there is a workmanship or defective fitting most times system pressure will show it. As far as two isolated heads what about the connection when you are done with the hydro test on two heads? Or hydrotest done at rough in and then cutting drops after ceiling install. Just saying think the test requirement could easily be abused and additional cost may be excessive. We are a code driven industry but still want our end users to consider they are getting value. First step of that value is providing quality workmanship and materials. Sprinkler systems have an enviable track record so we never want to compromise system integrity. If those two sprinklers are over a multi-million dollar clean room tool verses two sprinklers for a couple bathrooms in a Great Clips lease space I may look at it differently. Glad NFPA 13 has tried to clarify but ultimately it is up to the AHJ.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT