Hydraulic Calculation for 1 Sprinkler on Domestic?

6/25/2026

12 Comments

 
GC asked us to add (1) head to a dentist's office closet where they store the nitrous tanks. Not a big deal, done it before tapping off the domestic line. The AHJ asked for calcs to prove it will work. The existing building is not sprinklered.

What are your thoughts on this?

Is there a way to prove it's workable?

Is there a standard that stipulates what is and what's not acceptable?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
6/25/2026 06:05:29 am

Well we're definitely in a grey area. But AHJ made the request.

My advice: Do it as a 13D calc (2 most demanding sprinklers in a compartment) There is clearly only one in the compartment (and entire building).

Make sure to include domestic loss in your calculations. There are charts in 13/13R/13D that should show you the equivalent losses to add to the system riser for the domestic load (you count the number of sinks, toilets, showers, etc. and add up the losses).

Then offer that calculation.

It still might not be workable depending on the hazard the AHJ expects the nitrous tanks to be considered for.

Reply
Brian K. Fain
6/25/2026 08:29:12 am

A word of caution, we have been required to install a separate backflow preventer for this one sprinkler head in the past.

Reply
Kelley Stalder
6/25/2026 08:40:54 am

Isn't a backflow preventer required anyway for a dental office?

Reply
Brian
6/25/2026 08:45:54 am

Yes. They had one on the domestic feed (which we tapped into), but the AHJ required a separate one for our sprinkler head and piping.

Ben F
6/25/2026 08:32:32 am

I would think this falls under the limited area sprinkler system requirement in the IFC, which would require a calculation per NFPA 13. Not sure where you are located or what's locally adopted, but 2024 IFC section 903.3.8 lists the requirements. My concern would be if this is classified as a med gas room, which would be OH2. Limited area sprinkler is limited to LH and OH1.

Reply
Glenn Berger
6/25/2026 08:44:59 am

I actually like the AHJ asking this comment. Just want to make sure that there is sufficient pressure such that water will flow from the sprinkler.

Where is this sprinkler located with respect to other plumbing fixtures? If the sprinkler is located at the high point on the facility than there could be a problem. If the sprinkler is located in the basement with plumbing fixtures above, then no issues.

Reply
Blaine
6/25/2026 08:51:51 am

I’ve always thought that you had to do the whole building and can’t just put in a sprinkler wherever you wanted. Ref NFPA 13 2022 1.3.2. For me it came up when I wanted to put some residential sprinklers in my shop where I had easy access to the water lines in the overhead.

Reply
Jack G
6/25/2026 11:20:54 am

Tyco makes a domestic water shut off valve (RSV-1) installed after the split to the single sprinkler. It prioritizes the flow to the fire system so the full flow and pressure is available.
I would use a meter to perform a flow test at the tap, using the system gauge at the bfp for the static and residual..
Then you can use the full water supply.

Reply
Wes
6/26/2026 08:04:27 am

I believe the Tyco RSV-1 is only listed for residential use.

Reply
Jon N
6/26/2026 11:26:09 am

As a former AHJ, we required many "limited area sprinklers" to protection a localized hazard (boiler rooms, paint booths, flammable liquids rooms, etc.). These would typically be 1-2 sprinklers off the domestic supply. Since this was potable water, they would often use copper lines. Most often these were "pipe schedule" designs - up to two sprinklers supplied by 1-inch copper per NFPA 13 (2016 edition) - Section 23.7.2.2.1.

If you knew the pressure in the water supply, you could probably calculate the system, but I am not sure why that would be necessary. It is assumed that this is a very small room (closet-sized?) and 1-inch copper supplying 1/2-inch orifice sprinklers would be more than adequate.

Again, if the pressure is known (maybe add a gauge at the connection point to the water supply), calculate the friction loss through the copper pipe and fittings, and include the sprinkler flow at the minimum pressure - 7 psi for most (and there you have it, simple hand calculation). 10 by 10 spacing = 100 sq. ft. 100 sq. ft. times 0.15 (OH-1) = 15 GPM. (15 GPM / K5.6)^2 = 7 PSI.

Reply
Mark Harris
6/30/2026 02:31:33 pm

Comments have covered most of my thoughts and Jon N well summarized what we did long time ago when BOCA code required sprinklers in a specific area (plus small basements).

One thing we did have to check was that the water meter was same size as piping. Could have a 1" service pipe but 5/8 meter was installed.

Reply
David L Miller
7/1/2026 10:55:06 am

RE: NFPA 101:9.7.1.2

"Sprinkler piping serving not more than six sprinklers for any hazardous area shall be permitted to be connected directly to a domestic water supply system having a capacity sufficient to provide 0.15 gpm/ft2 (6.1 mm/min) throughout the entire enclosed area."

Because the requirement has a specific density requirement it must be hydraulically calculated.... Now, find a domestic supply in a building small enough not to require sprinklers that can supply six sprinklers at Ordinary Hazard Group 1 density (no Hose Stream required). Oh, and trace all of the piping and fittings all the way back to the city main where a flow test was done. May be less costly to fire-rate the room since the code requirement is usually either fire rate the room or provide sprinklers.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT