As more and more uses of AI builds occur - what are your thoughts on non-traditional or custom built hydraulic calculations?
It's possible that anyone today, even without AI, could do basic tree or loop systems using Excel or even manual calculations, though it's slower and more painful to create NFPA 13 forms and charts, and basic hydraulic calc programs pay for themselves - hence why we all use them. But as we go down the road with AI, what happens when someone has ChatGPT create the calcs? Or create a program that does its own calcs? If I'm an FPE EOR, I don't have the time to QC and validate individual programs and each supporting calculation to make sure it's right. I'm not an AHJ, but I would feel similarly to an AHJ. It's purely my opinion (worth nothing), but there's some inherent trust in the legacy calc programs that, as a reviewer, I'm not double-checking the calculation methods or QC'ing the program, but instead focusing my effort on making sure the inputs are appropriate. What are your thoughts/plans on addressing it when something rogue comes across your desk? Or has it already happened, and how did you handle it? I know of engineers that specified digitally-created submittals in the 2000s and 2010s, when CAD replaced hand-drawings. Is that something you see getting specified? Lots to untangle here but curious of your perspective from whatever role you have. Thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
10/12/2026 06:56:34 am
NFPA just says "Computer Program" or "Computer-generated", it does not state any listing or approval requirements (for hydraulics, water delivery is still the outlier).
Reply
Glenn Berger
10/12/2026 08:16:03 am
I am unsure if an AI generated drawing or calculations have come across my desk. I still review submittals as required and comment as necessary.
Reply
Anthony
10/12/2026 08:48:57 am
"If I'm an FPE EOR, I don't have the time to QC and validate individual programs and each supporting calculation to make sure it's right."
Reply
Ricardo Gonzales Jr
10/12/2026 08:54:07 am
As an EoR you need to validate the information. You should either have an abbreviated version on your laptop or know how to quickly hand calc a few of the numbers. As a former AHJ and EoR, I do quick hand calcs to verify the numbers from the start and spot work backwards (not every sprinkler or connection) to the source.
Reply
Wes
10/12/2026 08:57:33 am
I agree and I think this is probably where things will head.
Reply
Jack G
10/12/2026 10:02:38 am
I think its the EOR s responsibility to do a " check calc" with his/her own software as opposed to just reviewing the inputs.
Reply
Jack G
10/12/2026 10:07:34 am
Most reputable Fire protection hydraulic software has tree,loop, grid software to build the model submitted.
Reply
Dave L.
10/12/2026 10:51:08 am
Acting as EOR reviewing submittals for the owner/architect, my specs say calculations shall be performed on a computer utilizing an approved fire protection hydraulics program. With A1, I may need to begin clarifying what "approved" means. I also accept Excel, but I can't remember the last time someone has submitted that. Regardless of what program is utilized, I do scrutinize the calcs and look for different things, depending on if it is a standalone program with manual entry, or say, Autosprink. I might have a trainee re-run an entire calc, or spot-check certain sections. I always check water supply, elevations, flex drop length, etc. for unintentional (or intentional) deviation. Especially if there isn't much of a safety factor. In my case, I am not (yet) evaluating individual programs, but I evaluate the calcs on various factors, including my trust and familiarity with the submitting contractor.
Reply
Streeter
10/19/2026 11:51:56 am
I make it a point to do a gut check calc for all the projects I review. If things are wildly off I will do node to node checks and make sure things are square for friction loss, sizes, etc.
Reply