How to Test, Verify Dry System Meets Demand?

10/29/2025

6 Comments

 
Forward flow testing for dry systems As an AHJ, this seems like a simple question, but I cannot find an answer.

We are diligent in enforcing the annual forward flow for wet systems. So, how do we verify the available water supply meets the hydraulic GPM requirements for dry systems?

The annual dry trip test tells us only that water is available and the backflow device opens. We do have one occupancy that placed a shutoff valve ("slam valve") near the top of the riser. They close that valve for the annual test and trip the system, only allowing water in that small section of pipe where they also installed hose valves for the flow test with pitot readings. The valve is chained open normally.

​How do others measure GPM annually on dry systems to ensure it meets the designed system demand?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder link
10/29/2025 08:05:51 am

NFPA 25 Section 13.7 (26 ed.) states that the system flow rate needs to be achieved. You're not testing the water supply, per se, you're verifying that the valve will open at the system demand. If the water supply needs to be verified, that should be with a flow test per NFPA 291 or other modeling efforts.

Ideally, there is some valve setup that allows the testing (bypass at the FDC, hose valves, tee-valve into a Storz connection) to allow the test orifices to be attached to a hose monster or smooth bore orifice to get readings from. We have had to retrofit hose valves onto many risers to perform forward flow testing.

You should not have to test through the dry valve, just a point downstream of the backflow and prior to the dry system valve.

We do have a couple properties that allowed a tee above the dry valve and below an upper control valve that has a normally closed butterfly valve leading to a test header to accommodate both a forward flow test of the back flow but to also satisfy that the valve will also operate correctly at the system flow rate and required pressures. This is well above most of our other properties and definitely not the norm.

Reply
Randy Kimbro
10/29/2025 08:55:06 am

Dan, you hit on our issue directly with NFPA 25 Section 13.7.

13.7.2.1* All backflow preventers installed in fire protection
system piping shall be exercised annually by conducting a
forward flow test at a minimum flow rate of the system
demand.

When verifying that the valve will open at the system demand, the only way to do so is measuring flow with a pitot to ensure we are reaching system demand. We are stuck on how to do that annually for dry systems.

We have a couple systems with a monitored tee above the backflow which enables that testing. Are there other options for dry systems?

I respectfully disagree with using NFPA 291. That is for fire flow testing for hydrants, not risers.

Reply
Dan Wilder link
10/29/2025 09:28:28 am

The reference to 291 was for verification of water supply which is different than a forward flow test to verify the backflow works as intended. If I read the original post incorrectly, it was not my intent to mix the two.

There are no requirements to flow the system demand through any other valve other than the backflow, and nothing that prevents it either. The original installation "should" have provided means to test without major modifications to the system, if not, that needs to be changed. Beyond that, there is no other normal procedure we perform to comply with the forward flow test requirements regardless of systems downstream of the backflow.

Our primary is hose valves/Storz to smooth orifices & Pitot or Hose Monsters
Rarely a flow meter if installed.

Anthony
10/29/2025 08:20:41 am

Forward flow testing is to ensure the backflow preventer is working properly supplying the riser not making sure the riser is fictional. The trip test on the riser ensures then dry valve is fictional. When you add those two together as Dan says you should have a working system.

Reply
Jesse
10/29/2025 09:16:29 am

I think there are several issues here. First, the forward flow test is to ensure the BFP is functional, so not every system downstream of the BFP will have hose connections.

The trip test is to ensure the dry valve is operational.

I think if the concern is whether the water supply is able to support the dry system still, Dan's recommendation of conducting a hydrant flow test and then comparing the results to the original install flow test is the best bet.

Reply
Jonathan Joseph
10/29/2025 09:19:32 am

If they installed hose valves on the riser as mentioned, you should be able to achieve testing your backflow and system demand. For example if your system demand is 400gpm at the base of the riser and there are (2) 2 1/2 hose valves you should be able to meet the requirements. Very common nowadays to install mechanical tees with hose valves on risers. Or use a bypass around the FDC check valve and test header valve normally closed.
And also, where the water is going flow into is important in certain jurisdictions.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT