How do I know if these valves are open or closed without using the signage present that says OPEN?
Are these non-indicating valves, or am I missing something? Are these even allowed? Thanks in advance.
16 Comments
Pete H
7/9/2025 06:36:46 am
Try turning the valve to the right. If it won't turn, it's closed.
Reply
JP
7/9/2025 08:08:01 am
Is there no sight glass on the valve? The top left valve looks to have a sight glass. There should be a visual indicator of "SHUT" or "CLOSED"
Reply
Anthony
7/9/2025 08:29:36 am
Great catch Jesse, I agree that window should indicated open/closed. Now the quality and functionality of that unit I don't think we can comment on.
Reply
Glenn Berger
7/9/2025 08:16:18 am
If these valves are a wall-type PIV assemblies then would qualify as an indicating valves. The wall flange is what I am clueing in on.
Reply
Todd E Wyatt
7/9/2025 08:28:07 am
NFPA 13-2022 requires "listed indicating valves" unless the requirements of 16.9.3.2.1, 16.9.3.2.2, or 16.9.3.2.3 are met :
Reply
Brian F.
7/9/2025 08:44:11 am
WPIV, as stated, target window tells the story, also, are the tamper switches in operation? If so, they will send a trouble alarm if someone attempts to close a valve.
Reply
Jack G
7/9/2025 08:44:57 am
They are all indicating wall post indicator valves.
Reply
Franck
7/9/2025 08:48:37 am
Looks like wall PIV and as indicated by JO & Jesse, they probably have a window with the indication open/shut.
Reply
Tom R.
7/9/2025 09:55:12 am
Definitely appears to have indicating windows on the side. Also check clarity of sign and window. usually over time sign and window gets cloudy and faded. I make them usually touch up the sign and replace the window. All valves should be visible and inspected per NFPA 25. When they have their annual test this should be written up as a deficiency. Also the IFC requires tampers so chains and lock are not necessary; however most insurance companies still mandate chains. A key for the padlock could be put in the fire department lock box and tagged.
Reply
Jose R Figueroa
7/9/2025 10:04:29 am
These PIV valves are installed horizontally and must have a sight glass indicating whether they are OPEN or CLOSED. Follow Pete H's instructions for the annual inspections. These valves are equipped with chains and tamper-proof alarms.
Reply
Randy Kimbro
7/9/2025 12:20:10 pm
NFPA 13 (2020) states:
Reply
James Art, Fire Protection Engineer
7/9/2025 01:38:01 pm
The padlocks are often special "breakaway" locks,
Reply
7/9/2025 01:39:28 pm
Those valves are Outside Stem and Yoke valves. The OS & Y valve is a configuration common in control valves that serve fire sprinkler and standpipe systems. Also, they are common in several industrial applications. OS & Y means 'outside stem and yoke' or 'outside screw and yoke', and it has this name because of its distinctive design features. When the center stem is out (visible) the valve is open, no center stem, the valve is closed.
Reply
Jeff
7/13/2025 08:51:54 am
Do a main drain test on each valve, unlock the chain. Turn each wheel either way to decide which direction opens or closes.Some valves are left open, some are right open.Use a yellow paint pen and write the direction of OPEN with an ARROW on each wheel. Now you know that if the wheel doesn’t turn it’s fully open. Relock the chain.
Reply
Jose R Figueroa
7/13/2025 09:58:24 am
A+
Reply