How to Sprinkler Vertical Storage Carousel?

5/26/2021

7 Comments

 
We are on a project where they are installing these vertical storage carousels and will be storing miscellaneous vehicle parts and tires. I don't see anything within NFPA 13 specifically mentioning this equipment, so the current plan of action is to treat this equipment as multi-row racking. Since it is not practical to provide in-rack sprinklers for this equipment due to the moving parts, we are planning on protecting this equipment with ESFR sprinklers.

Does this ESFR approach seem appropriate? Is there any information that I am not considering?

​This is something that is new to me so any input will be greatly appreciated.

https://www.storevertical.com/products/vertical-storage-system/tire-carousel

https://www.storevertical.com/products/vertical-storage-system/shelving-carousel

​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Franck
5/26/2021 08:18:13 am

You should check FM Global data sheet 8.34 – Protection for Automatic Storage

Some general guidelines I am using myself (not an approved standard):

Carousel automated retrieval systems should be provided with automatic sprinkler protection inside of the enclosures.
For carousel units, up to a maximum of 7.5 m (25 ft), the sprinkler protection should be provided at the ceiling level of the units.
The sprinklers should be capable of supplying a flow of at least 115 l/min (30 gpm) over the entire unit in accordance with NFPA 13, Standard for the Installation of Sprinkler Systems.
The maximum spacing between sprinkler heads should be 2.4 m (8 ft) with a maximum covered area of 6 m2 (64 sq ft).
The sprinkler heads should be quick response ordinary temperature (70°C – 160°F) with a nominal K-factor of 160 (11.2).
Typically, at least one level of sprinklers should be installed in the vertical section at the highest point possible while remaining below the travel plane of the upper horizontal section.


For carousel storage above 7.5 m (25 ft), the ceiling protection indicated above should be supplemented with intermediate levels of quick response ordinary temperature (70°C – 160°F) rated sidewall sprinkler heads (or extended coverage sidewall sprinkler heads) with a nominal K-factor of 115 (8.0), installed at both ends of the unit and designed to deliver a minimum flow of 115 l/min (30 gpm) at the most remote intermediate level of sprinklers, with all of the sprinklers within the unit operating.
The intermediate levels should be spaced with a maximum of 3 m (10 ft) vertically, with no more than 4.5 m (15 ft) between the last level and the protected ceiling level of the carousel.

An alternative would be to remove the ceiling of the carousel so that the sprinkler heads located at the ceiling level can reach the inside of this storage arrangement.

If the space at the top of the carousel is limited, recessed sprinkler heads can be used


If the materials stored within the carousel are of high value and/or could result in a major business interruption if damaged, then a gaseous suppression system should be considered in addition to the sprinkler protection recommended in this standard.

Noncombustible containers should be used in the carousel whenever possible.

The carousel unit should be interlocked to automatically shut-down upon sprinkler operation (or heat/smoke detection activation).

Reply
Craig Hanson
5/26/2021 08:18:31 am

I have just completed a very intensive review for the same type of building. I had reached out to NFSA and NFPA for clarification and deign criteria. IF you want more information please contact me at [email protected]

Reply
CJ Bonczyk
5/26/2021 09:20:53 am

Many times when we have protected the ASRS/VLM units for tools storage we are bound by the FM Global guidelines outlined by Franck above. I would add the specific coordination with the manufacturer is heavily required. The deflector has specific distances such as 3-4 max from the carousel top. DO NOT penetrate the carousel yourself. The manufacturer will provide you will a couple options of where sprinklers can be placed. Space your sprinklers accordingly by code and ensure the penetrations are made by the manufacturer otherwise you will void the unit's warranty. Your penetration will need to be fire sealed and a steel escutcheon will need to be bolted to the top. Also a separate detection and control valve feeding the unit is required. We typically install the VSR Autotest flow switch that does not require water flow to test the system.

Regarding the tire carousel we have used in the past 2015 IFC requirements, as tires are classified as a High Hazard commodity. Working with AHJ's previously and utilizing Section 3206.2 the Extent and Type of Protection provision to limit the hazard to an area of a building separated by 1-hour fire-resistive rated construction. Door openings have a fire resistance rating and have magnetic door holders that release upon sprinkler water flow. We utilized NFPA 13 Table 18.4(d) K25.2 sprinklers calculated based on either the number of sprinklers per NFPA 13 Table 18.4(d) or the number of sprinklers in room pending the room size allows you to calculate 12 sprinklers. The tire storage carousel can also be discussed between the AHJ and FPE to determine an acceptable means of protection based on the local adopted code.

Reply
Fred Anderson link
9/20/2022 02:52:10 pm

We are designing a fire engine maintenance facility which will include a Vidir vertical tire carousel model HT54162-0563-12. This to be located in Washington DC using the 2019 NFPA 13 code.

Do you have any recommendations for this installation.

Reply
Kevin
5/26/2021 09:54:34 am

FM Global has Data Sheet 8-33 for Carousel Storage and Retrieval Systems as well. Not sure if the tire storage is addressed in there but is worth a look.

Reply
Dan Wilder
5/26/2021 09:59:39 am

These don't look enclosed per those links so you're likely looking at a possible ceiling only protection scheme unless a pipe can get into the center area then you may be able to have an attempt at some single/double level in-rack protection. The Case Study video of the tire carousel does show 2 levels of in-racks at about the 35 second mark.

Option I have used in the past is to coordinate a draft stop above the equipment to avoid the 15' extension of the high hazard density. As stated above, the FM guide is helpful for direction as long as the carousel falls into the specific descriptions within the document.

Reply
Aariz mudassir link
6/28/2024 12:31:19 pm

Automated Vertical Tire Storage Carousel. Dimensions: 17'10"H, 17'8"W, 7'8". Must hold up to 33" diameter tires. Capacity for

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT