How to Sprinkler Protect an Exposed Waffle Slab?

10/25/2022

7 Comments

 
I'm working on the renovation of an existing building with waffle slab construction.

As part of our scope, the client would like to sprinkler the space, and the architect was asking if we would be required to provide sprinkler coverage in each of the waffle slab pockets if they left the structure exposed.

Originally I thought we could treat the space as ceiling pockets, but since it's not an "architectural feature" I'm thinking the exceptions in NFPA 13 11.2.7.2 would not apply. The pockets created are roughly 3-ft x 3-ft wide, and the structure is 2-ft deep.

If we're using upright sprinklers, and they need to be installed 1"-12" below the "ceiling" (in this case, the slab?), taking a look through the obstruction/positioning tables, it seems like the structure would create obstructions and a head would be needed in every compartment?

Agree? Disagree?

Any insight would be appreciated.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Casey Milhorn
10/25/2022 08:09:23 am

I would recommend getting an official ruling from NFPA, and while you wait for that to come back (it can take awhile), I would get an informal interp from AFSA. I would argue this could be treated as concrete tee construction with no minimum deflector distance but with deflectors at a 1" minimum down from bottom of concrete "tee". If that doesn't fly. you can also classify this as obstructed construction, place a head at the center every 3rd to 5th pocket (depending on hazard and spacing), and keep deflector at 22" down from deck and no more than 2.5" above bottom of "tee". Sounds like you have a couple options here to avoid every pocket.

Reply
Yves Poulin
10/25/2022 08:14:09 am

Maybe if they drywall every pocket you will not need to sprinkler every waffle ?
If it's cost saving not sure

Reply
Eric R
10/25/2022 08:44:26 am

Depending on your occupancy class I think you could get away with a 9' x 12' or 12' x 12' sprinkler spacing pattern utilizing the obstructed construction rules.

From the 2016 edition of NFPA 13

8.6.4.1.2 Obstructed Construction
(2) Installed with the deflectors at or above the bottom of the structural member to a maximum of 22 in. (550 mm) below the ceiling/roof deck where the sprinkler is installed in conformance with 8.6.5.1.2

If you set your deflectors right at 22" down for the slab that would put them 2" above the bottom of the beams. Per 8.6.5.1.2 you are allowed to be 2.5" above the bottom of the beam as long as you are 1' away from it's edge. If the sprinkler is located in the center of each pocket then they should be at least 1' away from the edge of the beam if your pockets are nominally 3'x3'.

I would double check the pocket dimensions, and make sure you get the center-of-pocket to center-of-pocket distances to make sure your overall spacing conforms with your coverage area limitations based on the occupancy hazard.

Failing this, I also think you could likely consider the structure to be concrete tee construction, but if so, you'd want to get that approved by the AHJs involved.

Reply
Randy Rathert
10/25/2022 10:29:31 am

Nicely done. that makes for a complete analysis.

Reply
Jessica Lutz
10/25/2022 12:00:13 pm

...Precisely how I've seen it handled on a few projects.

Reply
Alex
10/25/2022 01:40:22 pm

Exactly how I've protected waffle ceilings before in the past! Well said.

Reply
Bobby V
10/27/2022 08:53:19 am

Sections taken from 2016 NFPA 13.

This type of construction falls into definition of obstructed construction, section 3.7.1, since the members impede heat flow.

Next, use one of the methods given in 8.6.4.1.2 for deflector placement in obstructed construction. You can use arrangement (2), but as Eric R mentions, since the deflector is 22" down from the deck, you then have to apply Table 8.6.5.1.2 to position the deflector to avoid water spray on the waffle. It then becomes a challenge to properly space sprinklers throughout the space while keeping the required distances away from the members.

I would recommend asking the AHJ for approval to use arrangement (5), which is used for concrete tee construction, because the depth of the tee does not matter.

There are other options...The architect could install cloud ceilings conforming to 8.15.24 to avoid sprinklers at the upper roof deck. Or he could just install a ceiling to cover the whole area, and then you would just have pendent sprinklers in the lower ceiling.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT