How to Interpret 2-Hour "Building" in NFPA 72?

5/20/2021

6 Comments

 
NFPA 72, 2016 Edition uses the phrase "2-hour fire-rated construction" in a few places; what does this refer to?

It's confusing to me since a variety of elements within the building could be 2-hour rated. For example, NFPA 72-2016 Section 24.3.13.7 states:

"Two-way in-building wired emergency communication systems shall have a pathway survivability of Level 2 or Level 3. Exception: Level 1 shall be permitted where the building is less than 2-hour fire-rated construction."

Buildings are not designated with a fire-rating, elements are. How do you interpret this?

​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
CJ Bonczyk
5/20/2021 08:42:54 am

SFPE has an article that talks about fire ratings/enclosures and pathway circuit survivability requirements. Not sure if this helps provide a little bit of clarification regarding a specific construction types.

https://www.sfpe.org/publications/magazine/fpeextra/fpeextra2017/fpeextraissue14

Reply
Todd E Wyatt
5/20/2021 08:53:50 am

SHORT ANSWER
A building which is "less than 2-hour fire-rated construction" would be of a Type of Construction of Type III, IV or V.

LONG ANSWER
Fire-resistance ratings (FRR) of buildings can be divided into (2) categories : Type of Construction and separation of adjacent spaces.

All buildings are assigned a Type of Construction (see IBC Ch 6) which asssigns a FRR of the "building elements" : primary structural frame (columns & beams), bearing walls (exterior and interior),floor constrcution, and roof construction. There are (5) Types : Type I (most stringent) to Type V. Type I & II are those in which the building elements are "noncombustible". Type III may have both noncombustible (e.g. masonry exterior walls) and combustible materials (e.g. wood framing). Type IV are mass timber or noncombustible building elements. Type V is all others. Each type has subsets (e.g. IA & IB) which have different FRR. The Type of Construction is determined by the Design Team based on the "allowables" (IBC Ch 5, max bldg height, max number of stories, and max area per story) based on the building's Occupancy Classification (IBC Ch 3).

The other FRR categories are assigning specific areas, rooms, and spaces protection by FRR assemblies (IBC Ch 7) such as fire walls, fire barriers, fire partitions, smoke barriers, smoke partitions, shaft enclosures, and horizontal assemblies based on hourly ratings of 0.5, 1, 2, 3, and 4 hours. Elevator hoistways may be protected by 1-hour shaft enclosures or by 2-hour shaft enclosure based on how many stories they connect (<4 or 4 or more) and by the FRR of the floor construction (Type of Const) they penetrate.

Reply
James
5/20/2021 08:57:53 am

Under that premise of a "building" being less than 2-hour, would a Type II-B building, without any rated partitions or barriers, be considered having 2-hour fire-resistance-rated construction?

Not trying to be argumentative, I'm just trying to understand. I haven't heard it presented that way, I've only known the later point for FRR assemblies.

Reply
Todd E Wyatt
5/21/2021 08:27:33 am

I neglected to include Type IIA (1-Hour) and Type IIB (0-Hour) with the above Type III, IV or V Types of Construction that would be less than 2-hours.

The FRR of individual rooms/spaces, and areas are not directly related to the building's Type of Construction. Depending on the building's Occupancy Classification(s) (e.g. Business, Storage, Mercantile), a Type IIA (1-hour) or Type IIB (0-hours) building could be 4 stories that would require its elevator hoistways, mechanical shafts, and interior exit stairways to all be protected by 2-hour FRR assemblies. These 2-hour FRR assemblies, if they were NOT load-bearing, would be required to be supported by 2-hour (floor) construction. These 2-hr floor constrcution would also be required to be supported by 2-hour columns and beams.

If instead, the elevator hoistways, mechanical shafts, and interior exit stairways are all independenlty load bearing, they indivdually would have a 2-hr FRR but all the surrounding building elements (primary structure, floor const, foof const) could be Type IIB and 0-hr rated. It seems counterintuitive to require 2-hour FRR elevator hoistways, mechanical shafts, and interior exit stairways with 0-Hr FRR building elements that theoretically would burn, fail, and collapse around these vertical elements.

sean
5/21/2021 07:46:21 pm

easiest way it that it is contained and isolated from the rest of the building, think shaft, stairways, mechanical / electrical rooms that are stacked

Reply
fire rated access doors and panels link
8/3/2021 08:52:35 am

The facts that have been discussed here are really important. Thank you so much for sharing a great post.


Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Dec '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT