We have an instance of "flowswitch cycling" on a new wet-pipe system. The RPZ backflow is thought to be causing the flow switch to fluctuate and, therefore, not get us the flow alarm in a timely manner or at all.
We have opened the manual high point air vent and flowed for several minutes with no success. Has anyone had this or found a solution to it? Potter has a technical bulletin on this but does not go into detail about how to resolve it. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
10/8/2024 06:47:19 am
Describe the system:
Reply
Glenn Berger
10/8/2024 08:15:14 am
In addition to Dan's response, I would add:
Reply
Derek Wallis
10/8/2024 08:27:19 am
We've delt with cycling flow switches in the past and it generally occurs on the tree type systems where air gets trapped at the end of the branchlines, compresses, then pushes back, causing the retard on the flow switch to reset. The way to fix a true cycling flow switch is by adding auto vent(s) or adding manual air vent lines at the end of the branchlines (similar to a dry system gang drain).
Reply
GAFFER
10/8/2024 08:34:38 am
again, describe the system.
Reply
Jack G
10/8/2024 10:22:36 am
Derek is on point. I ve found low incoming pressure to contribute the most. I use that to get the water company to allow the bfp to be on the discharge side of pumps.
Reply
Matthew Mueller
10/8/2024 10:59:07 am
Derick's point on the BFP causing issues as well. one manufacture in particular uses checks with a cam that won't allow full opening until a higher flow volume overcomes the "bump". Usually, one sprinkler flowing doesn't achieve what's necessary.