I have 6" and 8" sprinkler pipes that need to be supported by pipe stands at 26 ft.
What does NFPA 13 require to be done/designed for this situation? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
4/14/2026 07:30:46 am
NFPA 13 - 2025 Edition
Reply
anthony
4/14/2026 08:48:43 am
You're able to use 4'' pipe up to 26.8ft AFF per Table 17.5.3.1 NFAP 13-2025. I would however encourage you to reach out to a Unistrut/powerstrut supply company and get a custom solution. They should have a structural PE that can get involved and get you a more robust solution with supports that are interconnected and can handle more abuse than axially loaded pipe stands.
Reply
Moderator
4/14/2026 09:52:33 am
Just to clarify, with 4-inch to 8-inch diameter system pipe (being supported), a 4-inch diameter pipe stand can stand up to 14.7 feet, and a 6-inch diameter pipe stand can stand up to 26.8 feet in this table (Table 17.5.3.1(a) in NFPA 13-2025).
Reply
Anthony
4/14/2026 10:09:35 am
Yeah I got my columns mixed up and did mean 6'' pipe up to 26.8 feet.
Jack G
4/14/2026 08:51:11 am
I generally do a “ slenderness ratio calculation “ for the length of the column which you can find on line. I also implant the column at least 1/3 of the height which can be done with 2 pieces and flanges that meet at the floor line.
Reply
Ken Thackery
4/14/2026 10:03:26 am
I would depart from an NFPA solution and fabricate a pipe rack with tube steel. You can use a stud welder to attach. Can you add some context as to why this situation is occuring and why there is no structure above?
Reply