|
I'm hoping someone might be able to provide a little direction on the requirements of NFPA 13 2016 Section 23.4.4.8.1 (4) for hydraulic calculations.
We typically use 2"x2"x2 1/2" Vic IR Bullhead Tee directly on the welded grooved outlet. Per NFPA we should be including these fittings on the branch line, but we have always included the tee fitting on the 2 1/2" riser nipple because inside diameters are not typical to a 2" tee. We have been doing this for the longest time and recently received corrections from the local AHJ. Victaulic does not specify the frictional resistance - equivalent length of the NO. 104 Bullhead Tee fitting on the branch line. Have you come across this before, or any suggestions? I tried to create a new fitting type in HydraCalc, but was having trouble. Also, might be pointless since there is no data for this on Victaulic's cut sheets. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
5/16/2022 08:24:28 am
Treat the bullhead tee as a standard 2-1/2 tee, with reducer to the 2 inch pipe.
Reply
Joshua Mann
5/16/2022 11:15:59 am
I thought that could potentially be an option, but to include the fitting on the branch and not riser nipple, I would need to add another node at the reducing coupling? Is that the same way you would calculate it?
Reply
Dan Wilder
5/16/2022 08:39:21 am
Section 5.0 - Friction Flow Data for the No.104 (I'm assuming that is the fitting type you are referencing)
Reply
Joshua Mann
5/16/2022 11:18:55 am
Yes, that's the one. Not sure why they don't include an equivalent length for the 2" bullhead tee on the branch. They only provide the data on the run.
Reply
David Kendrick
5/16/2022 11:38:08 am
Victaulic 10.06
Mike
5/16/2022 09:57:54 am
For a reducing tee I'd be using the smaller diameter.
Reply
Brian Gerdwagen
5/16/2022 01:26:17 pm
2" tee on the line. Ignore the reducing part. If it was a 2 1/2" line to a 2" Riser Nipple, then use a 2" tee in the riser nipple. Smallest diameter governs.
Reply
Jack G
5/16/2022 03:33:27 pm
I think you might be trying to eliminate a node, for input reasons ?
Reply
Tracey D Bellamy
3/22/2023 03:06:24 pm
NFPA 13 requires the equivalent length for the loss associated with the tee is to be included in each side for the branch lines fed from the tee. This is based on the loss being associated with amount of water being turned which would be represented by the flow in the branch line on each side.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Oct '25 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
November 2025
PE PREP SERIES |
RSS Feed
