How to Calculate a Fire Pump Test Header Size?

2/15/2023

15 Comments

 
NFPA 20 says that if the test header supply main is more than 15 feet from the fire pump, it must be increased one pipe size or hydraulically calculated based on 150 percent of the rated pump capacity.

What form does the hydraulic calculation take?

Are we trying to determine if the main can flow 150 percent of the pump rating without running out of pressure?

How low a pressure would be acceptable?

Is this a one time calculation to size the main or is this a calculation that must be performed during each annual fire pump test?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Dan
2/15/2023 07:11:30 am

The appendix in the 22' Ed [A4.22.3.4(3)] has a worksheet for this scenario. As the calculation is based off a number (the pump rating) x a % of the capacity of the pump, one calculation is all that is required, and the test must meet this minimum. I've never done this before either...

That final number minus the pump discharge pressure (as the calculation is ran all the way back to the discharge flange of the pump) is your required pump discharge...if the pump discharge is higher than calculations then the pipe sizing and testing configuration (including number of hoses and length of hoses) is acceptable.

I would then suggest making a placard for this testing method, so future ITM companies perform the same test configuration and don't write up the pump as deficient because they tested with 3 hoses instead of 4 and used 100' hoses vs 50' and the couldn't get pitot pressures to work.

Reply
Jesse
2/15/2023 08:06:21 am

Dan's last comment about making up a placard is an excellent idea. I never thought about how helpful this would be.

Reply
Franck
2/15/2023 08:24:13 am

It is always good to give explanations for future reference. That avoids a lot of questions and misunderstanding.

Just like the provision of hydraulic system nameplates at base of each risers with detailed information on the sprinkler systems (design, hydraulic claculation results). This saves a lot of time for any further evaluation of the systems.

Anthony
2/15/2023 03:55:52 pm

I agree with the others, Dan has this down.

Glenn Berger
2/15/2023 08:46:37 am

I like the placard suggestion made by Dan above. This would be in addition to additional required documentation that is required to be provided.

As far as the question -- "how low pressure would a pressure be acceptable?" I would recommend following NFPA 291 Paragraph 4.6.6 for acceptable minimum (10 psi) in measuring flow with a pitot gauge.

Reply
Mike Morey
2/15/2023 09:07:03 am

I made a spreadsheet for this based on the annex form, whenever we run into one of these I have our guys run it and then put a note on the drawing that sizing is not increased per hydraulic calculation with a safety pressure of X. Ironically I've always said do the calculation because I've literally never had one fail, until a few months ago when i finally found a pump that it didn't work and we did have to do the up-size. That was a very small/low pressure vertical inline.

Reply
Kamran Khalid
3/28/2023 03:07:39 am

Can i also get the spreadsheet. I also need it for a project. You can email me. My email is [email protected]

Reply
Alan Barnhizer
4/25/2023 09:21:57 am

I would like to see your spreadsheet as well. Could you share it with me?

Reply
Robbie Jacobs
8/10/2023 11:50:30 am

Hello Mike. I know you have been bombarded for this I see, but can I get a copy of your spreadsheet?
email me at: [email protected].

Let's talk.

Compensation can be provided if you require.

Thanks!

Reply
Ryan Marx
7/9/2024 03:08:55 pm

This was very helpful. Can I also get the spread sheet? My email is [email protected]

Reply
Angela Sosnosky
4/21/2025 07:59:09 am

Would you please share this with me? [email protected]

Reply
Esteban Roldan
3/20/2026 12:54:11 pm

Hi Mike, If you still have the spreadsheet and are able to share, please send to [email protected]. Thank you!

Reply
Richard H
2/16/2023 11:38:34 am

Mike, Any chance I could get a copy of your spread sheet? I'm still struggling here. Thank you sir.

Reply
Andy Peter
4/19/2023 09:13:42 am

The spreadsheet from the annex *generally* makes sense to me. But I cannot reconcile the calculation for required Pitot Pressure P = (Q/29.83CD^2)^0.5 and the table and sample calc that shows the required pitot pressure as 18.

What am I missing?

Reply
Steve Maglione
7/15/2024 01:16:55 pm

Need to square rather than take the square root.

Q=29.84 x sqrt(P) x D^2 x C

sqrt(P)=Q/(29.84 x D^2 x C)

P=(Q/(29.84 x D^2 x C))^2

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT