|
Is there a preferred method of protecting a room with the sole purpose of storing oxygen cylinders?
FM-200, NOVEC, IG, water mist? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
Pete H
8/12/2024 07:17:32 am
Probably not FM-200 right now because it's being phased out.
Reply
Franck
8/12/2024 09:52:58 am
Novec 1230 may also be stopped in the very next future (for the fluorine issue similar to fluorine based foams - PFAS).
Reply
Joe Mc
8/12/2024 10:32:27 am
Please se the following website for the most up to date information related to FM 200 and FK 5-1-12
Pete H
8/12/2024 01:28:32 pm
Oh damn, that's not good. That was my answer when FM 200 got shut down. You wouldn't happen to know of a different foam system on the horizon, would you?
RyanO
8/12/2024 08:19:19 am
NFPA 55 addresses storage of compressed gas cylinders.
Reply
Aly Hussain
8/12/2024 08:23:56 am
same as all bottles of pressurized gases, the room has to be ventilated on one side at least of building facade. and the width of facade side to be twice the depth of the room. also, there is a chance to store upside roof or outside building.
Reply
Dan Wilder
8/12/2024 08:41:26 am
Liquid or Gas?
Reply
Chad
8/12/2024 08:44:23 am
I have only seen them wet sprinklered at OHII, or none at all if its a noncombustible room.
Reply
8/12/2024 08:47:18 am
Ordinary Hazard, no special fire sprinkler protection is needed. Compressed Gasses protection is found in the IFC Chapter 53. The environment of the room is very important. The danger is not the 02 but the pressure that the 02 is under and having that 02 further feed fire growth. In the event of a fire you want the cylinders to stay cool say that won't pop. Mist and fm200 system are will not achieve this is a sustained manner. Standard sprinklers and proper room conditions are what's needed.
Reply
Anthony
8/12/2024 09:12:37 am
I've only seen O2 rooms treated as a storage room. OH-1 or OH-2/HC-2.
Reply
Joe
8/12/2024 09:17:58 am
connected to the water purveyor so you can throw water at it all day long. Don't limit yourself with a finite amount of extinguishing agent.
Reply
Todd E Wyatt
8/12/2024 09:22:04 am
If this application is in a New Health Care occupancy per NFPA 101 Life Safety Code - 2012 (adopted by CMS for all hospital accepting Medicare and/or Medicaid funding), NFPA 101 references NFPA 99-2012.
Reply
Todd E Wyatt
8/12/2024 09:22:39 am
REFERENCES
Reply
Franck
8/12/2024 09:51:42 am
Normally, the simplest (and the costless) is sprinkler protection.
Reply
Franck
8/12/2024 09:54:30 am
Inert gas is not an option as they control the fire by reducing the oxygen content.
Reply
Jack G
8/12/2024 10:39:17 am
NFPA 99, 58, 55.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
September 2026
PE PREP SERIES |
RSS Feed
