I'm trying to establish a way to avoid dry valves/dry systems to protect trash and line chutes early in project development. I've heard of freezing issues due to roof venting or other ways that cold air can fill the chute (perhaps from the bottom when trash room doors may be open to the exterior during severe cold).
I know most or maybe all of these fabricated chutes come with fire sprinklers, but are they usually essentially built-in dry barrel sprinklers? If not, how can we ensure they won't freeze without using a dry system? The specific chute submittal or product information is usually not available until well after space for a dry valve should be set aside. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Glenn Berger
9/26/2025 08:13:40 am
You can use a horizontal dry sidewall sprinkler.
Reply
Lainey
9/26/2025 08:15:00 am
would an antifreeze loop be possible?
Reply
Thank Me Later
9/26/2025 08:34:17 am
https://www.victaulic.com/products/vicflex-dry-sprinkler-style-vs1/
Reply
Dan Wilder
9/26/2025 09:05:28 am
The issue is most trash chutes already come with a 1/2" FNPT connection and the 1/2" FNPT connection on the inside (a welded 1/2" union) and even a sprinkler on the interior at times. The discussion needs to start with the MFG to NOT place these welded connections and instead, install the base plate for the dry sprinkler connection. If that can't work, omit the sprinkler connection all together and field mount it.
Reply
danefre
9/26/2025 12:17:09 pm
To answer your question, use a dry VicFlex Pendent, fed from the floor system.
Reply
Jeff Ayers
9/26/2025 12:27:02 pm
All of the trash chutes on the projects I have worked on over the last 40 years have drywall sidewall heads. (they come installed that way and the sprinkler sub makes the connection)
Reply
Eric Ginder
9/26/2025 04:32:31 pm
Thank you for having the knowledge! I assumed this was the case after I thought about it but was not able to find any corroborating indication. I'm guessing the rumors I heard of freeze failure is exactly as you described - due to inadequate heat in the discharge room at the bottom.
Reply
Jesse
9/26/2025 12:50:08 pm
A dry HSW sprinkler could be a good option
Reply
Jack G
9/26/2025 03:52:10 pm
My opinion is that water in any area that is cold or erratic cold approaching freezing or below should never have water at the seat/ sprinkler head.
Reply
James Art, FPE
10/1/2025 10:44:03 am
A trash chute fire may set off fire sprinklers inside on several floor levels. Ideally the chute (not shoot! ;-)