How to Arrive at 2,000 sqft CMDA Design Area?

8/4/2026

8 Comments

 
I have a CMDA wet system, protecting solid-piled Group A Plastics storage. The storage height will be under 12 feet.

Under Section 21.3.3(a), I have been led to the density of 0.60 gpm/sqft in Column C, over a remote area of 2,500 sqft. The 2,500 sqft remote area is what's getting me; it seems cut and dry that in my situation, I am stuck there unless I have a closed storage array.

I wanted to verify against other people's interpretations: are there any other ways I am missing that would allow the area to be brought down to 2,000 sqft?

I primarily ask because I have seen other systems in the field with areas of 2,000 with densities 0.40, 0.50, 0.60, and I'm unsure of how those systems have gotten to that point with the current codes.

​For clarity, I am using the 2022 edition of NFPA 13. Any input would be appreciated. Thanks.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
8/4/2026 06:15:35 am

From the 2019 edition (you may have to update some reference numbers for 2022):

21.3 CMDA Sprinkler potection criteria for palletized, solid piled, bin box, shelf, or back to back shelf storage of plastic and rubber commodities.

21.3.5 For storage of Group A plastics between 5 ft and 12 ft in height, the installation requirements for extra hazard systems shall apply.

-

19.2.3.2.7 Extra Hazard Occupancies
19.2.3.2.7.1 For extra hazard occupancies with ceilings not exceeding 30 ft in height, the system area of sprinkler operation shall be permitted to be reduced b 25 percent without revising the density, but not to less than 2000 sq. ft. where one of the following conditions occurs:
1) High temp sprinklers are used
2) K11.2 sprinklers or larger are used.

Reply
Brett
8/4/2026 08:28:22 am

Those references from chapter 19 do not apply to OP's situation since their storage is not classified as an EH1 or EH2 hazard. Section 21.3.3.1 says that the area can only be reduced where either:

1) Table 21.3.3(a) says "EH1" or "EH2" and you use K-11.2 sprinklers or high temperature sprinklers.
2) Closed array storage.

Reply
Anonymous
8/4/2026 10:24:38 am

I interpreted 21.3.5 as referring to sprinkler spacing criteria, specifically Table 10.2.4.2.1(c), as 10.2.4.2.1(d) is spacing criteria for High-Piled Storage, which Chapter 3 defines as storage >12ft in height.

If it wasn't for 21.3.5 allowing the use of the Extra Hazard table, there would be no direction for spacing requirements on storage between 5 and 12 feet, but I don't think it allows you to call it Extra Hazard for the purpose of reducing the remote area below what is said in Chapter 21.

Reply
Dan Wilder
8/4/2026 07:57:13 am

Hasn't changed in the 2022 but there are now 2 separate sections to clarify that either condition allows the reduction
19.2.3.2.6 - High Temp Sprinklers
19.2.3.2.7 - K-11.2 or greater

Reply
Franck
8/4/2026 11:16:21 am


They have been using the miscellaneous table for storage up to 12 ft of group A plastic and ended up with the adjustments indicated avove.

But you should not consider it as an acceptable solution as these adjustments apply only for extra hazard occupancies. In your case, you are using the design equivalent to an EH Gr 2, but cannot use the adjustment that are only applicable for an occupancy and not for a commodity

Another explanation might be that they made the evaluation for a class IV commodity with a higher height of storage where the area of application is 2000 sq ft.

Reply
Jack G
8/4/2026 12:41:54 pm

Start with the hazard classification curve and take all the reductions like qr heads.
Then per chpt 21 apply reduction for high temperature heads and / or closed array storage. Should come up with a 2000sqft MRA.

Reply
Jack G
8/4/2026 12:44:58 pm

You should check the MeyerFire cheat sheet for area reduction from I think May of 2022 or so. That may help also

Reply
Anonymous
8/4/2026 01:00:05 pm

I have looked at the cheat sheet, the only note it has about remote area minimums for storage is to look at NFPA 13 for if High Temperature sprinklers may make a difference, on note 4 on the right.

Storage doesn't come with quick response reduction, and for Solid-Piled, you're only allowed high-temp(or high k-factor) reduction if your commodities density falls in accordance with EH1 or EH2 according to table 21.3.3(a).




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT