Does anyone know if there's a way to determine the water hammer created when a Fire Pump turns on (Hard Start)?
I have an existing facility that's about 60 years old with a lot of buried fire mains serving about 10-15 systems. They are on city water at about 55 psi static, and they want us to install a Diesel Fire Pump. Everything in the facility is Ordinary Hazard Group 2, with no plans to add on or change occupancy down the road. I've chosen a 1,500 gm diesel fire pump at 49 psi, but the owner is worried about blowing out the underground when the pump kicks on. The churn is 55 psi + the city at static 55 psi + 21% for pump overspeed gives us a maximum of around 133 psi that the pump could ever produce. Although it's not required, we plan to install a main discharge relief valve. Adding 10 psi more for the jockey pump, we could be up around 143 psi, and the owner is not comfortable with this. What are some options? Reduce the pump down to 1,000 GPM, 750 GPM? Reduce the pump's rated pressure to 35 PSI? We would need to adjust the PRV's to relieve at predetermined pressures. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
David Kendrick
11/2/2026 08:15:57 am
Verify the existing underground.
Reply
William Heuberger
11/9/2026 08:15:38 am
Water hammer occurs when a quick closing valve is closed too fast. High pressure does not cause water hammer, but can be a contributing factor to water hammer if the flow suddenly stops.
Reply
Glenn Berger
11/2/2026 08:18:54 am
A few questions first:
Reply
Glenn Berger
11/2/2026 10:01:20 am
Another potential solution is to add in a hydro-pneumatic surge tank.
Reply
Jack G
11/2/2026 11:20:50 am
I would use a flat curve pump along with a pump surge suppressor. The pressure I would use is so there is no more than 100 psi on the mains.
Reply
Helena Vrettou
11/2/2026 12:50:53 pm
What would I recommend?
Reply
Colin Lusher
11/2/2026 02:51:58 pm
Please don't ruin this forum with ChatGPT responses. We can all do that at home. We come here for real, thoughtful responses from real people. This response has all the hallmarks of AI, but if I'm wrong, my apologies.
Reply
Ed Glynn
11/2/2026 02:21:35 pm
My question starts with the systems are on existing city pressure at 55 PSI. What are the calcs for the existing sprinkler systems ad why at this point in time are the owners wanting to add a diesel fire pump.
Reply
Helena
11/2/2026 02:50:57 pm
Actually, I think we try to solve a problem from the end of the story.
Reply
Helena Vrettou
11/2/2026 02:53:27 pm
And I think the most interesting part is that the water hammer may not be the first problem to solve.
Reply
Mark Harris
11/2/2026 05:14:16 pm
Lots of extensive discussion so will keep it brief. First as several have questioned why a pump now if systems were designed on 55 PSI city pressure. Totally agree with that question. Second where is the sizing coming from? Are there private hydrants and sprinkler systems or just sprinkler systems?
Reply
Nimal Tissa Wijetunga
11/2/2026 10:37:26 pm
1)In my view, to settle the water hammer issue,you need to maintain maximum Velocity as 15 feet per second in all segment of the pipe network.
Reply
Streeter
11/3/2026 09:23:49 am
Not something that addresses the water hammer, as much as the fact that life safety systems need to be functional and work as designed. I would determine the fire pump size first off of the most demanding remote area and then subsequently address the water hammer issues where they might occur.
Reply
M.A
11/4/2026 07:30:38 am
From my point of view,
Reply