I am designing a 25.2k ESFR system in warehouse with purlins set on tapered beams with about 8" wide flanges spaced 20' on center. The last beam in the project area runs 1'-5" off the wall creating a small beam pocket along the length of the wall.
Current head spacing is 10'x10', and 18" below ceiling. The sprinklers adjacent to the beam are 3'-10" from centerline, or 5'-3" from the wall. This would require heads within the beam pocket, but the clearance between the wall and beam would obstruct sprinkler discharge. Are there any special exceptions that would allow heads to be omitted from the pocket? Or how could I approach this condition differently to meet code? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Arthur Gould
7/21/2026 08:32:08 am
I am interested in knowing the responses but I would be more concerned with the total 5'-3" off the wall than the pocket.
Reply
Chris Nelson
7/21/2026 09:33:35 am
I have experienced this and included ESFR underneath the pocket with shields because thats is what I believe code would require, it was also at the maximum height for ESFR (line 1 for 40' rack 45' ceiling), but I see that this not even half the height of my building so I would be more inclined to not do it. ( PS The contractor didnt like it, shocker)
Reply
Jack G
7/21/2026 11:27:13 am
Exceeding 5 foot off the wall is my main concern.
Reply
Kyle Wilcox
7/23/2026 11:31:25 am
Note that all ceiling-level ESFR sprinklers in a compartment must be 8 feet apart.
Reply
danefre
7/21/2026 12:06:07 pm
ESFR is an interesting choice for this building. What are you protecting that needs K25.2 ESFR at 12'-6ish AFF?
Reply
Colin B
7/21/2026 03:15:06 pm
This is an interesting job for us. The first section of the building is much higher ceiling heights using K25's and the owner wants the same style system in this next smaller storage area so they can have the same level of tenant flexibility as the first 1/3 of the building. That's the main reason for the ESFR K25's. we Explained a CMDA and he would rather stick with what is already installed in the other areas if possible
Reply
Dan Wilder
7/21/2026 08:29:43 pm
So...the new NFPA 13 2028 2nd Draft has a new section concerning this setup with a diagram. I can't copy the TerraView info so check it out as to intent.
Reply
Corey
7/22/2026 06:58:08 am
Thank you for these comments everyone. One alternative I considered would be to shift the line to 6' off the wall, then shorten head spacing along the line to 8'. This should allow heads to spray under the beam and to the wall, except for the corners where the beam is deepest. However, I'm unsure if i would need to provide an ESFR head in the corners or if NFPA allows for a smaller K-factor head.
Reply
Chris Lizakowski
7/22/2026 01:45:46 pm
Correct me if I am wrong but you can shift the one line 1'-0" making it so 5'-6" off the wall is your maximum distance. As long as you don't exceed 110 sq ft.
Reply
Kyle Wilcox
7/23/2026 11:03:49 am
Feels like an odd choice to use ESFR sprinklers in such a short building. Max storage height may be 6 or 8 feet?
Reply