We are a large metropolitan area with multiple universities that have been operating for decades with high levels of hazardous materials. They want to have separated control areas, but their building construction does not meet current requirements.
On one side we can only enforce the code that these were built to, which was BOCA or even no building code at the time, but on the other hand, there is a reason why control areas came about in the first place. As they cannot easily upgrade the structure to meet 2-hr requirements, I am planning on just using equivalent level of safety through sprinkler protection and other factors, but was wondering if anyone had experience doing enforcement like this? Is NFPA 45 enforceable here? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Berger
1/27/2025 08:08:31 am
We cannot tell you about the applicability of NFPA 45 in your jurisdiction.
Reply
Brett
1/27/2025 08:15:44 am
Regardless of whether NFPA 45 is adopted, it won't be applicable because NFPA 45 says that flammable or hazardous chemicals are outside its scope.
Reply
Brett, Not sure where you see the broad scope exclusion for flammable liquids and hazardous materials. NFPA 45 does genereally apply to these hazard categories. It does exclude chemical with a health, flammable or instability hazard rating of 0 and 1 which are the lowest hazard materials in those categories. It also excludes very small quantities, less than 1 gal of flammable/combustible liquid and less than 75 scf of flammable gas in a lab unit. There are ither specific exclusions as well. But to broadly say that it would not be applicable is not correct. That being said, NFPA 45 is not referenced by the I-Codes and would not be enforceable except where specifically adopted by the jurisdiction. In some states I have worked, the State Fire Marshal adopts NFPA Codes/Standards parallel to any I-Codes that are adopted by the city, county, state.... I agree with Glenn and NFPA 45 would serve as a good tool to bring these labs into come level of compliance. I am somewhat surprised that the university does not have some type of lab safety, fire safety champion to manage and advocate for concerns such as this.
Todd E Wyatt
1/27/2025 09:31:56 am
Review the CONTROL AREA requirements per the scoping Codes (e.g. IBC-2021 & IFC-2021).
Reply
Todd E Wyatt
1/27/2025 09:36:32 am
Since this is an existing building, review the International Existing Building Code (IEBC) Chapter 13 Performance Compliance Methods :
Reply
Todd E Wyatt
1/27/2025 12:20:57 pm
NFPA 45 Standard on Fire Protection for Laboratories Using Chemicals, a referenced standard, is referenced per the following scoping Codes (e.g. IBC-2021 & IFC-2021) :
Reply
Jack G
1/27/2025 11:04:46 am
Hard to answer without knowing specifics of the hazardous material.