MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How Tall is Storage Above & Below Mezzanine?

5/12/2023

10 Comments

 
So I've run into this a couple of places and I'm curious where other professionals land. You have a warehouse that has a mezzanine. Say the warehouse is 20'-0" tall and the height of the mezzanine is an even 10'-0".

You have 8'-0" of shelf storage underneath the mezzanine. You have 8'-0" of shelf storage on the mezzanine.

You are protecting under the mezzanine separately, but the mezzanine does not make up the full floor area of the entire warehouse. So there are open areas where you only have 8'-0" of storage to a taller 20'-0" building.

Does the storage over the mezzanine bring your storage up to 18'-0" or is it 8'-0" of storage?

It's 18'-0" over the floor, but 8'-0" over the floor of the mezzanine.

And there is protection beneath the mezzanine, but the storage under the mezzanine extends beyond the outline of the mezzanine. It's still only 8'-0" high, but now the ceiling height is different.

Anyway, any input or thoughts would be great. Code references always appreciated.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Anthony
5/12/2023 07:37:20 am

Depends how wide the mezzanine is. If it's under 15' then you have to cover it as if it was the adjacent hazard anyway so the area above the mezzanine is protected at 20' height requirements.

Generally speaking, if the spacing is similar and the calc's work them I'm going to let it stay as a single hazard covered at the higher rating. The field productivity will probably not be worth the material cost differences.

The area under the mezz should be treated as a lower(pun intended) hazard with the exception of heat transfer to adjacent rack storage. If the aisle is very narrow, then some judgment is needed to either change the storage configuration or add additional protection.

Reply
Dewayne Martinez
5/12/2023 08:33:30 am

I would treat it the same as Anthony.

Reply
Glenn Berger
5/12/2023 08:21:06 am

Looks like you have three different issues here:

System 1 is designed for the storage that occurs below the mezzanine. System 2 is designed for the storage on the mezzanine. System 3 is designed for the storage that occurs where there is no mezzanine.

Is the mezzanine floor solid construction or is the floor a grated material?

Reply
Dan Wilder
5/12/2023 08:44:41 am

They are considered separate areas.

Storage height from finished 1st floor = 8'
Ceiling height from finished 1st floor = 10' (below mezz)
Ceiling height from finished 1st floor = 20' (below roof deck)

Storage height from finished mezz floor = 8'
Ceiling height from finished mezz floor = 10' (below roof deck)

To confirm, no shelf/rack is taller than 8' in this scenario, just it's location.

Now the deciding factor is the mezzanine construction. If it is a solid mezz (pan deck/concrete/wood) this finalizes the separation and in either case, you have 8' of storage.

In the case of some (specifically auto parts stores are great at this) mezzanines that have open metal grating, that would trigger a total higher storage height of 18', especially if the shelving aligns above and below (and I have even seen the mezzanine have cutouts for those racks).

This creates a huge issue with shelf storage over 15' tall and I have been successful in using the lower protection as a level of in-rack protection splitting the storage. The owner did agree to place sheet metal below or plywood above to further separate the upper and lower storage areas.

Only other consideration is which NFPA 13 is being referenced as to where the square footage is assigned, but that was not your question.

Reply
Todd E Wyatt
5/12/2023 09:14:57 am

SUMMARY
2021 NFPA 13 references “MEZZANINE” (12) times but none include prescriptive requirements in determining the height of “storage above & below” a MEZZANINE.

EXPLANATION
The first step would be to verify that the MEZZANINE meets the definition and requirements (Area Limitations, Openness, Clear Height Above & Below) per the scoping Code (e.g. 2021 IBC, Section 505 MEZZANINES and Equipment Platforms). See REFERENCES below.

Assuming that the MEZZANINE meets the definition and requirements, the next step is to review the scoping Code (2021 IBC) references to “RACK STORAGE” & “HIGH-PILED (COMBUSTIBLE) STORAGE” to determine WHICH is applicable to your condition.

As it relates to “Fire Protection and Life Safety Systems”, 2021 IBC Chapter 9 Fire Protection and Life Safety Systems directs us to the 2021 International Fire Code (IFC) for additional requirements for “HIGH-PILED COMBUSTIBLE STORAGE.”

The 2021 IFC includes an entire chapter (32) on HIGH-PILED COMBUSTIBLE STORAGE ... “storage of combustible materials in closely packed piles or on pallets, in racks or on shelves where the top of storage is greater than 12 feet in height, or 6 feet for high-hazard commodities”.

Based on the referenced “8’-0” of storage”, we will assume that it is “RACK STORAGE” and not “HIGH-PILED (COMBUSTIBLE) STORAGE”

The 2021 IFC references RACK STORAGE in Chapter 32, 51, and 57 but none of these reference “MEZZANINES.”

Reply
Todd E Wyatt
5/12/2023 09:15:16 am

REFERENCES

2022 NFPA 13
Chapter 4 General Requirements
4.4 System Protection Area Limitations.
4.4.2
The floor area occupied by MEZZANINEs shall comply with 4.4.2.1, 4.4.2.2, or 4.4.2.3.
ENHANCED CONTENT
Subsection 4.4.2 clarifies where a MEZZANINE area needs to be tabulated as part of the floor area limitations specified in 4.4.1 and where it does not. Prior to these clarifications being added in the 2019 edition, it could have been interpreted that a system riser protecting a 52,000 ft² (4380 m²) area could also protect a MEZZANINE of unlimited size.
4.4.2.1
In a building with only one sprinkler system, the floor area occupied by MEZZANINEs shall not be included in the area limits of 4.4.1.
ENHANCED CONTENT
FAQ When determining the area limitations for a single floor, is the additional area occupied by MEZZANINEs required to be added to the floor area?
Paragraph 4.4.2.1 does not require the additional area occupied by the MEZZANINE to be counted against the area limitation. Exhibit 4.7 shows an example of the intent of this requirement. For high-piled storage, the area protected by one system riser cannot exceed 40,000 ft2 (3720 m2). When the area is being determined, the MEZZANINE area does not need to be added to the actual floor area.
4.4.2.2
In a building with more than one sprinkler system, if a MEZZANINE is located entirely within the same sprinkler system boundary as the sprinklers protecting the ceiling above, the floor area occupied by MEZZANINE(s) shall not be included in the area limits of 4.4.1.
4.4.2.3
In a building with more than one sprinkler system, if any portion of the MEZZANINE floor area is located outside the system boundary of the riser supplying the sprinklers under the MEZZANINE, the area of the MEZZANINE outside the boundary of the overhead system shall be added to the system area from which it is supplied, and the total system area shall meet the limits of 4.4.1.
ENHANCED CONTENT
For the 2019 edition of NFPA 13, new system protection area limitation requirements were added where MEZZANINEs are present. Prior to the 2019 edition, there was nothing to prevent an overhead sprinkler system from being installed to the area limitations of 4.4.1 and then supplying the underside of a MEZZANINE whose area far exceeded the overhead system’s boundary. For example, there was nothing to prevent a sprinkler system in a 1,000,000 ft2 (92,903 m2) building supplying a 52,000 ft2 (4830 m2) area at the roof from also supplying a 300,000 ft2 (27,870 m2) MEZZANINE. Now, with the new requirements, any MEZZANINE area that is outside the overhead system boundary must be added to the system protection area limitations and not exceed the limitations of 4.4.1. See Exhibit 4.8 for clarification of the requirements of 4.4.2.

Chapter 28 Plans and Calculations
28.5 Pipe Schedules.
28.5.1.5 Slatted Floors, Large Floor Openings, Mezzanines, and Large Platforms.
Buildings having slatted floors or large unprotected floor openings without approved stops shall be treated as one area with reference to pipe sizes, and the feed mains or risers shall be of the size required for the total number of sprinklers.
ENHANCED CONTENT
Fire spreads readily through grated or slatted floors. Therefore, an area with such divisions must be treated as a single fire area for sizing pipe.

Reply
Todd E Wyatt
5/12/2023 09:15:59 am

REFERENCES

2021 IBC
Chapter 5 General Building Heights and Areas
User note:
About this chapter: Chapter 5 establishes the limits to which a building can be built. Building height, number of stories and building area are specified in this chapter. Chapter 5 must be used in conjunction with the occupancies established in Chapter 3 and the types of construction established in Chapter 6. This chapter also specifies the impact that MEZZANINES, accessory occupancies and mixed occupancies have on the overall size of a building.

Section 505 MEZZANINES and Equipment Platforms
505.1 General
MEZZANINES shall comply with Section 505.2. Equipment platforms shall comply with Section 505.3.
505.2 MEZZANINES
A MEZZANINE or MEZZANINES in compliance with Section 505.2 shall be considered a portion of the story below. Such MEZZANINES shall not contribute to either the building area or number of stories as regulated by Section 503.1. The area of the MEZZANINE shall be included in determining the fire area. The clear height above and below the MEZZANINE floor construction shall be not less than 7 feet (2134 mm).
505.2.1 Area Limitation
The aggregate area of a MEZZANINE or MEZZANINES within a room shall be not greater than one-third of the floor area of that room or space in which they are located. The enclosed portion of a room shall not be included in a determination of the floor area of the room in which the MEZZANINE is located. In determining the allowable MEZZANINE area, the area of the MEZZANINE shall not be included in the floor area of the room.
Exceptions:
1. The aggregate area of MEZZANINES in buildings and structures of Type I or II construction for special industrial occupancies in accordance with Section 503.1.1 shall be not greater than two-thirds of the floor area of the room.
2. The aggregate area of MEZZANINES in buildings and structures of Type I or II construction shall be not greater than one-half of the floor area of the room in buildings and structures equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1 and an approved emergency voice/alarm communication system in accordance with Section 907.5.2.2.
3. The aggregate area of a MEZZANINE within a dwelling unit that is located in a building equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2 shall not be greater than one-half of the floor area of the room, provided that:
3.1. Except for enclosed closets and bathrooms, the MEZZANINE shall be open to the room in which such MEZZANINE is located;
3.2. The opening to the room shall be unobstructed except for walls not more than 42 inches (1067 mm) in height, columns and posts; and
3.3. Exceptions to Section 505.2.3 shall not be permitted.
505.2.1.1 Aggregate Area of MEZZANINES and Equipment Platforms
Where a room contains both a MEZZANINE and an equipment platform, the aggregate area of the two raised floor levels shall be not greater than two-thirds of the floor area of that room or space in which they are located. The area of the MEZZANINE shall not exceed the area determined in accordance with Section 505.2.1.
505.2.2 Means of Egress
The means of egress for MEZZANINES shall comply with the applicable provisions of Chapter 10.
505.2.3 Openness
A MEZZANINE shall be open and unobstructed to the room in which such MEZZANINE is located except for walls not more than 42 inches (1067 mm) in height, columns and posts.
Exceptions:
1. MEZZANINES or portions thereof are not required to be open to the room in which the MEZZANINES are located, provided that the occupant load of the aggregate area of the enclosed space is not greater than 10.
2. A MEZZANINE having two or more exits or access to exits is not required to be open to the room in which the MEZZANINE is located.
3. MEZZANINES or portions thereof are not required to be open to the room in which the MEZZANINES are located, provided that the aggregate floor area of the enclosed space is not greater than 10 percent of the MEZZANINE area.
4. In industrial facilities, MEZZANINES used for control equipment are permitted to be glazed on all sides.
5. In occupancies other than Groups H and I, which are no more than two stories above grade plane and equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, a MEZZANINE having two or more exits or access to exits shall not be required to be open to the room in which the MEZZANINE is located.

Reply
Todd E Wyatt
5/12/2023 09:16:49 am

REFERENCES

2021 IBC

Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.1 General
Automatic sprinkler systems shall comply with this section.
903.1.1 Alternative Protection
Alternative automatic fire-extinguishing systems complying with Section 904 shall be permitted instead of automatic sprinkler system protection where recognized by the applicable standard and approved by the fire code official.
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.
Exception: Spaces or areas in telecommunications buildings used exclusively for telecommunications equipment, associated electrical power distribution equipment, batteries and standby engines, provided that those spaces or areas are equipped throughout with an automatic smoke detection system in accordance with Section 907.2 and are separated from the remainder of the building by not less than 1-hour fire barriers constructed in accordance with Section 707 or not less than 2-hour horizontal assemblies constructed in accordance with Section 711, or both.
903.2.7 Group M
903.2.7.1 HIGH-PILED STORAGE
An automatic sprinkler system shall be provided in accordance with the International Fire Code in all buildings of Group M where storage of merchandise is in HIGH-PILED or RACK STORAGE arrays.

Section 905 Standpipe Systems
905.1 General
Standpipe systems shall be provided in new buildings and structures in accordance with Sections 905.2 through 905.11. In buildings used for HIGH-PILED COMBUSTIBLE STORAGE, fire protection shall be in accordance with the International Fire Code.

Section 907 Fire Alarm and Detection Systems
907.1 General
This section covers the application, installation, performance and maintenance of fire alarm systems and their components.
907.2.15 HIGH-PILED COMBUSTIBLE STORAGE Areas
An automatic smoke detection system shall be installed throughout HIGH-PILED COMBUSTIBLE STORAGE areas where required by Section 3206.5 of the International Fire Code.

Section 910 Smoke and Heat Removal
910.2.2 HIGH-PILED COMBUSTIBLE STORAGE
Smoke and heat removal required by Table 3206.2 of the International Fire Code for buildings and portions thereof containing HIGH-PILED COMBUSTIBLE STORAGE shall be installed in accordance with Section 910.3 in unsprinklered buildings. In buildings and portions thereof containing HIGH-PILED COMBUSTIBLE STORAGE equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, a smoke and heat removal system shall be installed in accordance with Section 910.3 or 910.4. In occupied portions of a building equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, where the upper surface of the story is not a roof assembly, a mechanical smoke removal system in accordance with Section 910.4 shall be installed.

Reply
Todd E Wyatt
5/12/2023 09:17:30 am

REFERENCES

2021 IFC
Chapter 32 HIGH-PILED COMBUSTIBLE STORAGE
User note:
About this chapter: Chapter 32 provides guidance for reasonable protection of life from hazards associated with the storage of combustible materials in closely packed piles or on pallets, in racks or on shelves where the top of storage is greater than 12 feet in height, or 6 feet for high-hazard commodities. It provides requirements for identifying various classes of commodities; and general fire and life safety features including storage arrangements, smoke and heat venting, fire department access and housekeeping and maintenance. This chapter attempts to define the potential fire severity and, in turn, determine fire and life safety protection measures needed to control and in some cases suppress a potential fire. This chapter does not cover miscellaneous combustible material storage as regulated in Section 315.

Section 3201 General
3201.1 Scope
HIGH-PILED COMBUSTIBLE STORAGE shall be in accordance with this chapter. In addition to the requirements of this chapter, the following material-specific requirements shall apply:
1. Aerosols shall be in accordance with Chapter 51.
2. Flammable and combustible liquids shall be in accordance with Chapter 57.
3. Hazardous materials shall be in accordance with Chapter 50.
4. Storage of combustible paper records shall be in accordance with NFPA 13.
5. Storage of combustible fibers shall be in accordance with Chapter 37.
6. General storage of combustible material shall be in accordance with Chapter 3.

3201.3 Construction Documents
10. Type of fire protection systems.
14. Additional information regarding required design features, commodities, storage arrangement and fire protection features within the high-piled storage area shall be provided at the time of permit, where required by the fire code official.

Section 3206 General Fire Protection and Life Safety Features
3206.1 General
Fire protection and life safety features for high-piled storage areas shall be in accordance with Sections 3206.2 through 3206.11.

Section 3208 Rack Storage
3208.1 General
Rack storage shall be in accordance with Section 3206 and this section. Bin boxes exceeding 5 feet (1524 mm) in any dimension shall be regulated as rack storage.
3208.1.1 Storage Racks
The design and installation of storage racks shall be in accordance with the International Building Code.
3208.2 Fire Protection
Where automatic sprinklers are required by Table 3206.2, an approved automatic sprinkler system shall be installed throughout the building or to 1-hour fire barriers constructed in accordance with Section 707 of the International Building Code. Openings in such fire barriers shall be protected by opening protectives having a 1-hour fire protection rating. The design and installation of the automatic sprinkler system and other applicable fire protection shall be in accordance with Section 903.3.1.1 and the International Building Code.
3208.2.1 Plastic Shelves
Storage on plastic shelves shall be protected by approved specially engineered fire protection systems.
3208.2.2 Racks With Solid Shelving
Racks with solid shelving having an area greater than 20 square feet (1.9 m2), measured between approved flue spaces at all four edges of the shelf, shall be in accordance with this section.
Exceptions:
1. Racks with mesh, grated, slatted or similar shelves having uniform openings not more than 6 inches (152 mm) apart, comprising not less than 50 percent of the overall shelf area, and with approved flue spaces are allowed to be treated as racks without solid shelves.
2. Racks used for the storage of combustible paper records, with solid shelving, shall be in accordance with NFPA 13.
3208.2.2.1 Fire Protection
Fire protection for racks with solid shelving shall be in accordance with NFPA 13.

Reply
Franck
5/12/2023 09:23:17 am

Answer is in NFPA 13

If you have open steel gratings, you have to consider the mezzanine floor as walkways.

26.9 Special Design for Palletized, Solid-Piled, Bin Box, or Shelf Storage of Class I Through Class IV Commodities.
26.9.1 Bin Box and Shelf Storage.
26.9.1.1 Bin box and shelf storage that is over 12 ft (3.7 m) but not in excess of the height limits of 21.2.1 and that is provided with walkways at vertical intervals of not over 12 ft (3.7 m) shall be protected with automatic sprinklers under the walkway(s).

26.9.1.2 Protection shall be as follows:

(1) Ceiling design density shall be based on the total height of storage within the building as provided in Chapter 21.

(2) Automatic sprinklers under walkways shall be designed to maintain a minimum discharge pressure of 15 psi (1.0 bar) for the most hydraulically demanding six sprinklers on each level. Walkway sprinkler demand shall not be required to be added to the ceiling sprinkler demand. Sprinklers under walkways shall not be spaced more than 8 ft (2.4 m) apart horizontally.

This means that in your case, you need a design for a 18 ft storage height in the mezzanine area (at the ceiling level) + sprinklers between the shelves underneath the mezzanine, designed as indicated above.

The remaining of the building is fine for a storage up to 8 ft. But I would recommend, in that case, to protect the entire building for an 18 ft high storage, just in case they want to extend the mezzanine later on.

Sprinklers installed under open gratings should be of the intermediate level/rack storage type or otherwise shielded from the discharge of overhead sprinklers.
The shielding is required to prevent cold soldering of the thermal element from the discharge of the overhead sprinkler, resulting in a delay in operation of the sprinkler.

The purpose of the sprinklers underneath the walkway is to accomplish the following:
• Reduce the likelihood of horizontal fire spread under the walkway
• Protect any storage in the walkway
• Help control the fire in the shelves

If the mezzanine is solid floor (no open shelves), then you need to protect the ceiling level for a storage up to 8 ft, and underneath the mezzanine for a storage up to 8 ft.
In that case, a minimum free space of 18 in. (45 cm) should be maintained between the top of storage and the sprinkler deflector position (ceiling level as well as under the mezzanine).

You can also check:
NFPA Research Foundation – Impact of elevated walkways in storage on sprinkler protection – Phase 1 – March 2020.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT