FM Data Sheet 8-30 Having To Do With Roll Carpet Storage - on Table 1, how many sprinklers on a line do we calculate when we have 30 heads?
NFPA 13 does not cover roll carpet storage, and the NFPA 13 Equivalency Clause allows us to use FM Global. Take a look below, and the only thing I can not figure out is if I am required to discharge 30 K11.2 sprinklers @ 7.0 psi, how many open sprinklers would I calculate on a line? Maybe 7 sprinklers on 4 lines with 2 sprinklers on one line? It has to be in writing somewhere, but I can not find it! Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Pete H
6/18/2026 06:37:53 am
It should be in writing on Data Sheets 2-0 or 8-9 as per section 2.4.2 of Data Sheet 8-30.
Reply
anthony
6/18/2026 07:55:02 am
I think you need "Table 1. Determining the Number of Sprinklers Per Branch Line for Ceiling Sprinkler System Hydraulic Calculation" from FMDS 8-9 specifically equation 1
Reply
Pete H
6/18/2026 08:16:54 am
This answer nails it, looking at the most updated 8-9 the chart and equation are there.
Reply
Dennis Wilson
6/18/2026 09:37:40 am
This is how i have always used the FM design area chart.
Reply
Pete H
6/18/2026 12:43:33 pm
Doesn't it depend if it's unobstructed or obstructed construction?
Reply