We have an EH1 dry system, and will be installing the inspector's test manifold with 4 outlets.
We know that it's 2 outlets from the two remote branch lines, but I do not see in NFPA 13 if we should tie the line together so only 1 Inspector's Test Valve (ITV) would need to be operated to flow all 4 outlets, or if we'd install 2 ITV's valves next to each other, 1 valve for each remote line so the air is exhausting through each line independently. Any input would be appreciated! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
3/13/2026 08:15:19 am
Someone will need to correct me if I am totally off-base here!
Reply
Glenn
3/13/2026 08:47:36 am
I got this one incorrect. Water Delivery Calculations Section 8.2.4.3.
Reply
3/13/2026 08:23:41 am
My approach has been the lower picture and, in my mind, follows the wording from the standard:
Reply
M. Newell
3/13/2026 08:26:02 am
You would likely have 2 ITV. See Figure A.8.2.4.4. My thought is if you combined them together with a single valve you are limiting the flow to that single pipe vs taking the dual flow paths.
Reply
Donnie Brewer
3/13/2026 08:27:41 am
I think you are fine with option 1 by interconnecting the two providing you meet the time requirements for activation of the dry system. You only need water flow from a single sprinkler of the most demanding type head for the remote inspector test vale.
Reply
David Kendrick
3/13/2026 08:28:10 am
Likely to have better performance exhausting air/nitrogen from a single point.
Reply
Matt Hamilton
3/13/2026 08:30:03 am
Your second option is the correct way. You would have two ITV's installed, one for each two outlet manifold. 2022 NFPA 13 Figure A8.2.3.7 in the appendix shows it fairly well.
Reply
Jack G
3/13/2026 03:48:48 pm
2 nd way is how I d do it.
Reply
Dave S
3/16/2026 10:58:04 am
I agree with the others choosing option 2 as it will give the best chance of meeting delivery times by exhausting air the fastest. But it does bring up some questions that I've always wondered but haven't had a chance to test in the field or via one of the water delivery programs: